GE Multilin
F60 Feeder Protection System
5-137
5 SETTINGS
5.4 SYSTEM SETUP
5
•
PMU 1 POWER TRIGGER REACTIVE
: This setting specifies the pickup threshold for the reactive power of the
source. For single-phase power, 1 pu is a product of 1 pu voltage and 1 pu current, or the product of nominal second-
ary voltage, the VT ratio and the nominal primary current. For the three-phase power, 1 pu is three times that for a sin-
gle-phase power. The comparator applies a 3% hysteresis.
•
PMU 1 POWER TRIGGER APPARENT
: This setting specifies the pickup threshold for the apparent power of the
source. For single-phase power, 1 pu is a product of 1 pu voltage and 1 pu current, or the product of nominal second-
ary voltage, the VT ratio and the nominal primary current. For the three-phase power, 1 pu is three times that for a sin-
gle-phase power. The comparator applies a 3% hysteresis.
•
PMU 1 POWER TRIGGER PKP TIME
: This setting can be used to filter out spurious conditions and avoid unneces-
sary triggering of the recorder.
•
PMU 1 POWER TRIGGER DPO TIME
: This setting can be used to extend the trigger after the situation returned to
normal. This setting is of particular importance when using the recorder in the forced mode (recording as long as the
triggering condition is asserted).
Figure 5–51: POWER TRIGGER SCHEME LOGIC
j) DF/DT TRIGGERING
PATH: SETTINGS
SYSTEM SETUP
PHASOR MEASUREMENT...
PMU 1 TRIGGERING
PMU 1 df/dt TRIGGER
PMU 1 df/dt
TRIGGER
PMU 1 df/dt TRIGGER
FUNCTION: Disabled
Range: Enabled, Disabled
MESSAGE
PMU 1 df/dt TRIGGER
RAISE: 0.25 Hz/s
Range: 0.10 to 15.00 Hz/s in steps of 0.01
MESSAGE
PMU 1 df/dt TRIGGER
FALL: 0.25 Hz/s
Range: 0.10 to 15.00 Hz/s in steps of 0.01
MESSAGE
PMU 1 df/dt TRIGGER
PKP TIME: 0.10 s
Range: 0.00 to 600.00 s in steps of 0.01
MESSAGE
PMU 1 df/dt TRIGGER
DPO TIME: 1.00 s
Range: 0.00 to 600.00 s in steps of 0.01
MESSAGE
PMU 1 df/dt TRG BLK:
Off
Range: FlexLogic operand
MESSAGE
PMU 1 df/dt TRIGGER
TARGET: Self-Reset
Range: Self-Reset, Latched, Disabled
MESSAGE
PMU 1 df/dt TRIGGER
EVENTS: Disabled
Range: Enabled, Disabled
847011A1.CDR
SETTINGS
PMU 1 POWER
TRIGGER FUNCTION:
Enabled = 1
PMU 1 PWR TRIG BLK:
Off = 0
AND
SETTINGS
PMU 1 POWER TRIGGER ACTIVE:
RUN
SETTINGS
PMU 1 POWER TRIGGER DPO TIME:
t
DPO
FLEXLOGIC OPERAND
PMU 1 POWER TRIGGER
FLEXLOGIC OPERANDS
PMU 1 FREQ TRIGGER
PMU 1 VOLT TRIGGER
PMU 1 CURR TRIGGER
PMU 1 ROCOF TRIGGER
SETTING
PMU 1 USER TRIGGER:
Off = 0
OR
FLEXLOGIC OPERAND
PMU 1 TRIGGERED
abs(P) > ACTIVE PICKUP
abs(P) > ACTIVE PICKUP
abs(P) > ACTIVE PICKUP
OR
abs(P) > 3*(ACTIVE PICKUP)
abs(Q) > REACTIVE PICKUP
abs(Q) > REACTIVE PICKUP
abs(Q) > REACTIVE PICKUP
abs(Q) > 3*(REACTIVE PICKUP)
S > APPARENT PICKUP
S > APPARENT PICKUP
S > APPARENT PICKUP
S > 3*(APPARENT PICKUP)
SETTINGS
PMU 1 SIGNAL SOURCE:
ACTIVE POWER, PA
ACTIVE POWER, PB
ACTIVE POWER, PC
3P ACTIVE POWER, P
REACTIVE POWER, QA
REACTIVE POWER, QB
REACTIVE POWER, QC
3P REACTIVE POWER, Q
APPARENT POWER, SA
APPARENT POWER, SB
APPARENT POWER, SC
3P APPARENT POWER, S
PMU 1 POWER TRIGGER REACTIVE:
PMU 1 POWER TRIGGER APPARENT:
to STAT bits of
the data frame
SETTINGS
PKP
t
0
PMU 1 POWER TRIGGER PKP TIME:
0
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...