5 SETTINGS
5.4 SYSTEM SETUP
5
•
PMU1 PHS-1
to
PMU1 PHS-14
: These settings specify synchrophasors to be transmitted from the superset of all syn-
chronized measurements. The table outlines available synchrophasor values.
These settings allow for optimizing the frame size and maximizing transmission channel usage, depending on a given
application. Select “Off” to suppress transmission of a given value.
•
PMU1 PHS-1 NM
to
PMU1 PHS-14 NM
: These settings allow for custom naming of the synchrophasor channels. Six-
teen-character ASCII strings are allowed as in the CHNAM field of the configuration frame. These names are typically
based on station, bus, or breaker names.
•
PMU1 A-CH-1
to
PMU1 A-CH-16
: These settings specify any analog data measured by the relay to be included as a
user-selectable analog channel of the data frame. Up to 16 analog channels can be configured to send any FlexAnalog
value from the relay. Examples include frequency, rate of frequency change, active and reactive power, per phase or
three-phase power, power factor, temperature via RTD inputs, and THD. The configured analog values are sampled
concurrently with the synchrophasor instant and sent as 32-bit floating-point values scaled to Engineering units.
•
PMU1 A-CH-1 NM
to
PMU1 A-CH-16 NM
: These settings allow for custom naming of the analog channels. Sixteen-
character ASCII strings are allowed as in the CHNAM field of the configuration frame.
•
PMU1 D-CH-1
to
PMU1 D-CH-16
: These settings specify any digital flag measured by the relay to be included as a
user-selectable digital channel of the data frame. Up to 16 digital channels can be configured to send any FlexLogic
operand from the relay. The configured digital flags are sampled concurrently with the synchrophasor instant. These
values are mapped into a two-byte integer number, with byte 1 LSB corresponding to the digital channel 1 and byte 2
MSB corresponding to digital channel 16.
•
PMU1 D-CH-1 NM
to
PMU1 D-CH-16 NM
: These settings allow for custom naming of the digital channels. Sixteen-
character ASCII strings are allowed as in the CHNAM field of the configuration frame.
•
PMU1 D-CH-1 NORMAL STATE
to
PMU1 D-CH-16 NORMAL STATE
: These settings allow for specifying a
normal
state
for each digital channel. These states are transmitted in configuration frames to the data concentrator.
C37.118 PMU 1 CONFIGURATION
PATH: SETTINGS
SYSTEM SETUP
PHASOR MEASUREMENT
BASIC CONFIGURATION
PMU 1
PMU 1 BASIC CONFIGU-
RATION
37.118 PMU 1 CONFIGURATION
PMU 1 FORMAT
: This setting selects whether synchrophasors are reported as 16-bit integers or 32-bit IEEE floating point
numbers. This setting complies with bit-1 of the FORMAT field of the IEEE C37.118 configuration frame. This setting
applies to synchrophasors only; the user-selectable FlexAnalog channels are always transmitted as 16-bit integer values.
SELECTION MEANING
Va
First voltage channel, either Va or Vab
Vb
Second voltage channel, either Vb or Vbc
Vc
Third voltage channel, either Vc or Vca
Vx
Fourth voltage channel
Ia
Phase A current, physical channel or summation as per the source settings
Ib
Phase B current, physical channel or summation as per the source settings
Ic
Phase C current, physical channel or summation as per the source settings
Ig
Fourth current channel, physical or summation as per the source settings
V1
Positive-sequence voltage, referenced to Va
V2
Negative-sequence voltage, referenced to Va
V0
Zero-sequence voltage
I1
Positive-sequence current, referenced to Ia
I2
Negative-sequence current, referenced to Ia
I0
Zero-sequence current
37.118 PMU 1
CONFIGURATION
PMU 1 FORMAT:
Integer
Range: Integer, Floating-point
MESSAGE
PMU 1 STYLE:
Polar
Range: Polar, Rectangularr
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...