F-2
F60 Feeder Protection System
GE Multilin
F.1 DEVICE PROFILE DOCUMENT
APPENDIX F
F
Requires Application Layer Confirmation:
Never
Always
When reporting Event Data
When sending multi-fragment responses
Sometimes
Configurable
Timeouts while waiting for:
Data Link Confirm:
None
Fixed at ____
Variable
Configurable
Complete Appl. Fragment:
None
Fixed at ____
Variable
Configurable
Application Confirm:
None
Fixed at 10 s
Variable
Configurable
Complete Appl. Response:
None
Fixed at ____
Variable
Configurable
Others:
Transmission Delay:
No intentional delay
Need Time Interval:
Configurable (default = 24 hrs.)
Select/Operate Arm Timeout:
10 s
Binary input change scanning period:
8 times per power system cycle
Analog input change scanning period:
500 ms
Counter change scanning period:
500 ms
Frozen counter event scanning period:
500 ms
Unsolicited response notification delay:
100 ms
Unsolicited response retry delay
configurable 0 to 60 sec.
Sends/Executes Control Operations:
WRITE Binary Outputs
Never
Always
Sometimes
Configurable
SELECT/OPERATE
Never
Always
Sometimes
Configurable
DIRECT OPERATE
Never
Always
Sometimes
Configurable
DIRECT OPERATE – NO ACK
Never
Always
Sometimes
Configurable
Count
>
1
Never
Always
Sometimes
Configurable
Pulse On
Never
Always
Sometimes
Configurable
Pulse Off
Never
Always
Sometimes
Configurable
Latch On
Never
Always
Sometimes
Configurable
Latch Off
Never
Always
Sometimes
Configurable
Queue
Never
Always
Sometimes
Configurable
Clear Queue
Never
Always
Sometimes
Configurable
Explanation of ‘Sometimes’:
Object 12 points are mapped to UR Virtual Inputs. The persistence of Virtual Inputs is
determined by the
VIRTUAL INPUT X TYPE
settings. Both “Pulse On” and “Latch On” operations perform the same func-
tion in the UR; that is, the appropriate Virtual Input is put into the “On” state. If the Virtual Input is set to “Self-Reset”,
it will reset after one pass of FlexLogic. The On/Off times and Count value are ignored. “Pulse Off” and “Latch Off”
operations put the appropriate Virtual Input into the “Off” state. “Trip” and “Close” operations both put the appropriate
Virtual Input into the “On” state.
Table F–1: DNP V3.00 DEVICE PROFILE (Sheet 2 of 3)
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...