5-178
F60 Feeder Protection System
GE Multilin
5.6 GROUPED ELEMENTS
5 SETTINGS
5
d) PHASE INSTANTANEOUS OVERCURRENT
(ANSI 50P, IEC PIOC)
PATH: SETTINGS
GROUPED ELEMENTS
SETTING GROUP 1(6)
PHASE CURRENT
PHASE IOC 1(8)
The phase instantaneous overcurrent element may be used as an instantaneous element with no intentional delay or as a
definite time element. The input current is the fundamental phasor magnitude. For timing curves, see the publication Instan-
taneous Overcurrent Element Response to Saturated Waveforms in UR-Series Relays (
Figure 5–71: PHASE INSTANTANEOUS OVERCURRENT 1 SCHEME LOGIC
PHASE IOC1
PHASE IOC1
FUNCTION: Disabled
Range: Disabled, Enabled
MESSAGE
PHASE IOC1 SIGNAL
SOURCE: SRC 1
Range: SRC 1, SRC 2, SRC 3, SRC 4
MESSAGE
PHASE IOC1
PICKUP: 1.000
pu
Range: 0.000 to 30.000 pu in steps of 0.001
MESSAGE
PHASE IOC1 PICKUP
DELAY: 0.00
s
Range: 0.00 to 600.00 s in steps of 0.01
MESSAGE
PHASE IOC1 RESET
DELAY: 0.00
s
Range: 0.00 to 600.00 s in steps of 0.01
MESSAGE
PHASE IOC1 BLOCK A:
Off
Range: FlexLogic operand
MESSAGE
PHASE IOC1 BLOCK B:
Off
Range: FlexLogic operand
MESSAGE
PHASE IOC1 BLOCK C:
Off
Range: FlexLogic operand
MESSAGE
PHASE IOC1
TARGET: Self-reset
Range: Self-reset, Latched, Disabled
MESSAGE
PHASE IOC1
EVENTS: Disabled
Range: Disabled, Enabled
827033A8.CDR
AND
AND
AND
SETTING
1 = Enabled
Function
SETTING
= IA
Source
= IC
SETTINGS
= Off
Block A
= Off
Block B
= Off
Block C
SETTING
Pickup
RUN
IA > Pickup
RUN
IB > Pickup
RUN
IC > Pickup
= IB
SETTINGS
Pickup Delay
T
PKP
T
RST
Reset Delay
T
PKP
T
RST
T
PKP
T
RST
OR
FLEXLOGIC OPERANDS
PHASE IOC1 A PKP
PHASE IOC1 A DPO
PHASE IOC1 B PKP
PHASE IOC1 B DPO
PHASE IOC1 C PKP
PHASE IOC1 C DPO
PHASE IOC1 PKP
FLEXLOGIC OPERAND
PHASE IOC1 A OP
PHASE IOC1 B OP
PHASE IOC1 C OP
FLEXLOGIC OPERANDS
OR
PHASE IOC1 OP
FLEXLOGIC OPERAND
AND
PHASE IOC1 DPO
FLEXLOGIC OPERAND
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...