E-2
F60 Feeder Protection System
GE Multilin
E.1 IEC 60870-5-104
APPENDIX E
E
When using an unbalanced link layer, the following Application Service Data Unit (ASDU) types are returned in class 2
messages (low priority) with the indicated causes of transmission:
The standard assignment of ASDUs to class 2 messages is used as follows:
A special assignment of ASDUs to class 2 messages is used as follows:
5.
APPLICATION LAYER
Transmission Mode for Application Data:
Mode 1 (least significant octet first), as defined in Clause 4.10 of IEC 60870-5-4, is used exclusively in this companion
standard.
Common Address of ASDU:
One Octet
Two Octets
Information Object Address:
One Octet
Structured
Two Octets
Unstructured
Three Octets
Cause of Transmission:
One Octet
Two Octets (with originator address). Originator address is set to zero if not used.
Maximum Length of APDU:
253
(the maximum length may be reduced by the system.
Selection of standard ASDUs:
For the following lists, the boxes indicate the following:
– used in standard direction;
– not used;
– cannot be
selected in IEC 60870-5-104 standard.
Process information in monitor direction
<1> := Single-point information
M_SP_NA_1
<2> := Single-point information with time tag
M_SP_TA_1
<3> := Double-point information
M_DP_NA_1
<4> := Double-point information with time tag
M_DP_TA_1
<5> := Step position information
M_ST_NA_1
<6> := Step position information with time tag
M_ST_TA_1
<7> := Bitstring of 32 bits
M_BO_NA_1
<8> := Bitstring of 32 bits with time tag
M_BO_TA_1
<9> := Measured value, normalized value
M_ME_NA_1
<10> := Measured value, normalized value with time tag
M_NE_TA_1
<11> := Measured value, scaled value
M_ME_NB_1
<12> := Measured value, scaled value with time tag
M_NE_TB_1
<13> := Measured value, short floating point value
M_ME_NC_1
<14> := Measured value, short floating point value with time tag
M_NE_TC_1
<15> := Integrated totals
M_IT_NA_1
<16> := Integrated totals with time tag
M_IT_TA_1
<17> := Event of protection equipment with time tag
M_EP_TA_1
<18> := Packed start events of protection equipment with time tag
M_EP_TB_1
<19> := Packed output circuit information of protection equipment with time tag
M_EP_TC_1
<20> := Packed single-point information with status change detection
M_SP_NA_1
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...