5-182
F60 Feeder Protection System
GE Multilin
5.6 GROUPED ELEMENTS
5 SETTINGS
5
b) NEUTRAL TIME OVERCURRENT
(ANSI 51N, IEC PTOC)
PATH: SETTINGS
GROUPED ELEMENTS
SETTING GROUP 1(6)
NEUTRAL CURRENT
NEUTRAL TOC1(4)
The neutral time overcurrent element can provide a desired time-delay operating characteristic versus the applied current
or be used as a simple definite time element. The neutral current input value is a quantity calculated as 3Io from the phase
currents and may be programmed as fundamental phasor magnitude or total waveform RMS magnitude as required by the
application.
MESSAGE
NEUTRAL IOC8
MESSAGE
NEUTRAL
DIRECTIONAL OC1
MESSAGE
NEUTRAL
DIRECTIONAL OC2
NEUTRAL TOC1
NEUTRAL TOC1
FUNCTION: Disabled
Range: Disabled, Enabled
MESSAGE
NEUTRAL TOC1 SIGNAL
SOURCE: SRC 1
Range: SRC 1, SRC 2, SRC 3, SRC 4
MESSAGE
NEUTRAL TOC1
INPUT: Phasor
Range: Phasor, RMS
MESSAGE
NEUTRAL TOC1
PICKUP: 1.000
pu
Range: 0.000 to 30.000 pu in steps of 0.001
MESSAGE
NEUTRAL TOC1
CURVE: IEEE Mod Inv
Range: See OVERCURRENT CURVE TYPES table
MESSAGE
NEUTRAL TOC1
TD MULTIPLIER: 1.00
Range: 0.00 to 600.00 in steps of 0.01
MESSAGE
NEUTRAL TOC1
RESET: Instantaneous
Range: Instantaneous, Timed
MESSAGE
NEUTRAL TOC1 BLOCK:
Off
Range: FlexLogic operand
MESSAGE
NEUTRAL TOC1
TARGET: Self-reset
Range: Self-reset, Latched, Disabled
MESSAGE
NEUTRAL TOC1
EVENTS: Disabled
Range: Disabled, Enabled
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...