5-184
F60 Feeder Protection System
GE Multilin
5.6 GROUPED ELEMENTS
5 SETTINGS
5
•
System unbalances under heavy load conditions
•
Transformation errors of current transformers (CTs) during double-line and three-phase faults
•
Switch-off transients during double-line and three-phase faults
The positive-sequence restraint must be considered when testing for pickup accuracy and response time (multiple of
pickup). The operating quantity depends on how test currents are injected into the relay (single-phase injection):
(EQ 5.17)
Figure 5–75: NEUTRAL IOC1 SCHEME LOGIC
d) NEUTRAL DIRECTIONAL OVERCURRENT
(ANSI 67N, IEC PDEF/PTOC)
PATH: SETTINGS
GROUPED ELEMENTS
SETTING GROUP 1(6)
NEUTRAL CURRENT
NEUTRAL DIRECTIONAL OC1(2)
NEUTRAL
DIRECTIONAL OC1
NEUTRAL DIR OC1
FUNCTION: Disabled
Range: Disabled, Enabled
MESSAGE
NEUTRAL DIR OC1
SOURCE: SRC 1
Range: SRC 1, SRC 2, SRC 3, SRC 4
MESSAGE
NEUTRAL DIR OC1
POLARIZING: Voltage
Range: Voltage, Current, Dual, Dual-V, Dual-I
MESSAGE
NEUTRAL DIR OC1 POL
VOLT: Calculated V0
Range: Calculated V0, Aux. Voltage (VX)
MESSAGE
NEUTRAL DIR OC1 OP
CURR: Calculated 3I0
Range: Calculated 3I0, Measured IG
MESSAGE
NEUTRAL DIR OC1 POS-
SEQ RESTRAINT: 0.063
Range: 0.000 to 0.500 in steps of 0.001
MESSAGE
NEUTRAL DIR OC1
OFFSET: 0.00
Ω
Range: 0.00 to 250.00
Ω
in steps of 0.01
MESSAGE
NEUTRAL DIR OC1 FWD
ECA: 75° Lag
Range: –90 to 90° in steps of 1
MESSAGE
NEUTRAL DIR OC1 FWD
LIMIT ANGLE: 90°
Range: 40 to 90° in steps of 1
MESSAGE
NEUTRAL DIR OC1 FWD
PICKUP: 0.050 pu
Range: 0.006 to 30.000 pu in steps of 0.001
MESSAGE
NEUTRAL DIR OC1 REV
LIMIT ANGLE: 90°
Range: 40 to 90° in steps of 1
I
op
1
3
---
3
K
–
(
)
×
x
I
injected
=
FLEXLOGIC OPERANDS
NEUTRAL IOC1 FUNCTION:
NEUTRAL IOC1 PICKUP:
NEUTRAL IOC1 SOURCE:
NEUTRAL IOC1 BLOCK:
NEUTRAL IOC1 DPO
NEUTRAL IOC1 OP
NEUTRAL IOC1 PKP
RUN
AND
827035A5.CDR
SETTING
SETTING
Enabled=1
SETTING
SETTING
I_0
Off=0
SETTINGS
NEUTRAL IOC1
RESET DELAY :
NEUTRAL IOC1
PICKUP DELAY :
t
PKP
t
RST
3(
I
_0 - K
I
_1 ) PICKUP
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...