5-36
F60 Feeder Protection System
GE Multilin
5.2 PRODUCT SETUP
5 SETTINGS
5
When a 0 value is involved in a change, the changes to the
MODBUS TCP PORT NUMBER
setting take effect when the
F60 is restarted.
Do not set more than one protocol to the same TCP/UDP port number, as this results in unreliable operation of
those protocols.
i) PROTOCOL
The Protocol menu setting allows selection of one of the following protocols: DNP 3.0, IEC60870-104, or IEC60870-103.
For any change to take effect, restart the unit.
The table shows which of DNP 3.0, IEC 60870-5-104, IEC 60870-5-103, and IEC 61850 protocols are operational on the
RS232, RS485, and Ethernet ports. It shows all possible combinations of the
PROTOCOL
and
DNP CHANNEL 1(2) PORT
set-
tings.
Table 5–6: PORT AND PROTOCOL COMBINATIONS
PROTOCOL
SETTING
DNP CHANNEL 1(2) PORT
SETTINGS
RS232
RS485
ETHERNET
DNP
Channel 1: Eth TCP
Channel 2: Eth TCP
Modbus
Modbus
DNP, Modbus, IEC 61850
Channel 1: Eth TCP
Channel 2: none
Modbus
Modbus
DNP, Modbus, IEC 61850
Channel 1: none
Channel 2: Eth TCP
Modbus
Modbus
DNP, Modbus, IEC 61850
Channel 1: Eth UDP
Channel 2: none
Modbus
Modbus
DNP, Modbus, IEC 61850
Channel 1: Eth TCP
Channel 2: RS485
Modbus
DNP
DNP, Modbus, IEC 61850
Channel 1: Eth TCP
Channel 2: RS232
DNP
Modbus
DNP, Modbus, IEC 61850
Channel 1: Eth UDP
Channel 2: RS485
Modbus
DNP
DNP, Modbus, IEC 61850
Channel 1: Eth UDP
Channel 2: RS232
DNP
Modbus
DNP, Modbus, IEC 61850
Channel 1: RS485
Channel 2: Eth TCP
Modbus
DNP
DNP, Modbus, IEC 61850
Channel 1: RS232
Channel 2: Eth TCP
DNP
Modbus
DNP, Modbus, IEC 61850
Channel 1: RS485
Channel 2: RS232
DNP
DNP
Modbus, IEC 61850
Channel 1: RS232
Channel 2: RS485
DNP
DNP
Modbus, IEC 61850
Channel 1: RS485
Channel 2: none
Modbus
DNP
Modbus, IEC 61850
IEC 104
Modbus
Modbus
IEC 104, Modbus, IEC 61850
IEC 103
Modbus
IEC 103
Modbus, IEC 61850
NOTE
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...