GE Multilin
F60 Feeder Protection System
5-267
5 SETTINGS
5.7 CONTROL ELEMENTS
5
d) BREAKER FLASHOVER
PATH: SETTINGS
CONTROL ELEMENTS
MONITORING ELEMENTS
BREAKER FLASHOVER 1(2)
The detection of the breaker flashover is based on the following condition:
1.
Breaker open,
2.
Voltage difference drop, and
3.
Measured flashover current through the breaker.
Furthermore, the scheme is applicable for cases where either one or two sets of three-phase voltages are available across
the breaker.
BREAKER
FLASHOVER 1
BKR 1 FLSHOVR
FUNCTION: Disabled
Range: Disabled, Enabled
MESSAGE
BKR 1 FLSHOVR SIDE 1
SRC: SRC 1
Range: SRC 1, SRC 2, SRC 3, SRC 4
MESSAGE
BKR 1 FLSHOVR SIDE 2
SRC: None
Range: None, SRC 1, SRC 2, SRC 3, SRC 4
MESSAGE
BKR 1 STATUS CLSD A:
Off
Range: FlexLogic operand
MESSAGE
BKR 1 STATUS CLSD B:
Off
Range: FlexLogic operand
MESSAGE
BKR 1 STATUS CLSD C:
Off
Range: FlexLogic operand
MESSAGE
BKR 1 FLSHOVR V PKP:
0.850 pu
Range: 0.000 to 1.500 pu in steps of 0.001
MESSAGE
BKR 1 FLSHOVR DIFF V
PKP: 1000 V
Range: 0 to 100000 V in steps of 1
MESSAGE
BKR 1 FLSHOVR AMP
PKP: 0.600 pu
Range: 0.000 to 1.500 pu in steps of 0.001
MESSAGE
BKR 1 FLSHOVR PKP
DELAY: 0.100 s
Range: 0.000 to 65.535 s in steps of 0.001
MESSAGE
BKR 1 FLSHOVR SPV A:
Off
Range: FlexLogic operand
MESSAGE
BKR 1 FLSHOVR SPV B:
Off
Range: FlexLogic operand
MESSAGE
BKR 1 FLSHOVR SPV C:
Off
Range: FlexLogic operand
MESSAGE
BKR 1 FLSHOVR BLOCK:
Off
Range: FlexLogic operand
MESSAGE
BKR 1 FLSHOVR
TARGET: Self-reset
Range: Self-reset, Latched, Disabled
MESSAGE
BKR 1 FLSHOVR
EVENTS: Disabled
Range: Disabled, Enabled
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...