C-4
F60 Feeder Protection System
GE Multilin
C.2 SERVER DATA ORGANIZATION
APPENDIX C
C
C.2.6 MMXU: ANALOG MEASURED VALUES
A limited number of measured analog values are available through the MMXU logical nodes.
Each MMXU logical node provides data from a F60 current and voltage source. There is one MMXU available for each con-
figurable source (programmed in the
SETTINGS
SYSTEM SETUP
SIGNAL SOURCES
menu). MMXU1 provides data
from F60 source 1, and MMXU2 provides data from F60 source 2.
MMXU data is provided in two forms: instantaneous and deadband. The instantaneous values are updated every time a
read operation is performed by a client. The deadband values are calculated as described in IEC 61850 parts 7-1 and 7-3.
The selection of appropriate deadband settings for the F60 is described in chapter 5 of this manual.
IEC 61850 buffered and unbuffered reporting capability is available in all MMXU logical nodes. MMXUx logical nodes pro-
vide the following data for each source:
•
MMXU1.MX.TotW: three-phase real power
•
MMXU1.MX.TotVAr: three-phase reactive power
•
MMXU1.MX.TotVA: three-phase apparent power
•
MMXU1.MX.TotPF: three-phase power factor
•
MMXU1.MX.Hz: frequency
•
MMXU1.MX.PPV.phsAB: phase AB voltage magnitude and angle
•
MMXU1.MX.PPV.phsBC: phase BC voltage magnitude and angle
•
MMXU1.MX.PPV.phsCA: Phase CA voltage magnitude and angle
•
MMXU1.MX.PhV.phsA: phase AG voltage magnitude and angle
•
MMXU1.MX.PhV.phsB: phase BG voltage magnitude and angle
•
MMXU1.MX.PhV.phsC: phase CG voltage magnitude and angle
•
MMXU1.MX.A.phsA: phase A current magnitude and angle
•
MMXU1.MX.A.phsB: phase B current magnitude and angle
•
MMXU1.MX.A.phsC: phase C current magnitude and angle
•
MMXU1.MX.A.neut: ground current magnitude and angle
•
MMXU1.MX.W.phsA: phase A real power
•
MMXU1.MX.W.phsB: phase B real power
•
MMXU1.MX.W.phsC: phase C real power
•
MMXU1.MX.VAr.phsA: phase A reactive power
•
MMXU1.MX.VAr.phsB: phase B reactive power
•
MMXU1.MX.VAr.phsC: phase C reactive power
•
MMXU1.MX.VA.phsA: phase A apparent power
•
MMXU1.MX.VA.phsB: phase B apparent power
•
MMXU1.MX.VA.phsC: phase C apparent power
•
MMXU1.MX.PF.phsA: phase A power factor
•
MMXU1.MX.PF.phsB: phase B power factor
•
MMXU1.MX.PF.phsC: phase C power factor
C.2.7 PROTECTION AND OTHER LOGICAL NODES
The following list describes the protection elements for all UR-series relays. The F60 relay will contain a subset of protec-
tion elements from this list.
•
PDIF: bus differential, transformer instantaneous differential, transformer percent differential, current differential
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...