7-12
F60 Feeder Protection System
GE Multilin
7.1 COMMANDS
7 COMMANDS AND TARGETS
7
•
Message
: "An attempt to contact the Radius server has failed"
•
Latched target message
: No.
•
Description of problem
: The RADIUS authentication server is unavailable.
•
What to do
: Verify network connectivity and try again.
d) WRONG TRANSCEIVER MESSAGES
Description: The type of SFP does not match the CPU type.
T-type CPU = All ports support fiber SFPs only
Type: minor
Target: latched
Message: "WRONG TRANSCEIVER"
A webpage "SFP Transceiver Information" is provided. This page displays the type of the SFP in it. This data is to be used
with the CPU type to know the cause of the problem.
e) SFP X MODULE FAIL MESSAGES
Description: A faulty SFP or unplugging the SFP would generate this self test.
Type: minor
Target: self reset
Message: SFP MODULE x FAIL
The webpage "SFP Transceiver Information" described in the previous section applies for this self test as well. The "SFP
Module Fail" has higher priority and it suppresses the "Ethernet Fail" target message. The "SFP MODULE FAIL FUNC-
TION" setting enables/disables this self test. The target for this self test is priority-based, with the third one being the high-
est priority. For example, if all three SFP modules fail, then the third SFP target is activated. If the third SFP module failure
resolves, then the second SFP target is activated.
HARDFIBER SELF-TEST ERROR MESSAGES
In addition to those provided by the standard UR-series devices, the UR devices implement HardFiber self-tests. These are
listed below. Any abnormal diagnostic condition indicated by the LEDs or the critical failure relay also results in a self-test
message, so troubleshooting is described here. For other relays, such at the B95
Plus
, see that product’s instruction manual.
Equipment Mismatch Major Self-Test
Description: The number or type of installed hardware modules does not match the order code stored in the CPU. The stan-
dard UR-series Equipment Mismatch self-test is extended to cover the possible presence of a Process Card.
Severity: Protection is not available and all contact outputs and shared outputs are de-asserted.
If this message appears, check all modules against the order code. Ensure they are inserted properly, and cycle the control
power. If a module has intentionally been added or removed use the
Update Order Code
command to notify the relay that
the current module configuration is correct.
Module Failure Major Self-Test
Description: UR-series device module hardware failure detected.
Severity: Protection is not available and all contact outputs and shared outputs are de-asserted.
If this message appears, contact the factory and supply the failure code noted in the display. Text in the message identifies
the failed module (for example, H81). If operated on a Process Card failure, the Module Fail self-test seals-in (latches) till
the UR-series device is restarted.
SERVER UNAVAILABLE
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...