6-26
F60 Feeder Protection System
GE Multilin
6.3 METERING
6 ACTUAL VALUES
6
The above actual values are displayed without the corresponding time stamp as they become available per the recording
rate setting. Also, the recording post-filtering setting is applied to these values.
6.3.11 PMU AGGREGATOR
PATH: ACTUAL VALUES
METERING
PHASOR MEASUREMENT UNIT
PMU AGGREGATOR 1
Actual values for the IEC 61850-90-5 PDU size are provided. These values allow you to know the approximate Ethernet
frame size for the data streams from each aggregator. This can help to estimate network loading. The PDU size shown in
the displays does not include the Ethernet, UDP, or IP layers. PDU sizes approaching approximately 1500 bytes result in
fragmented data frames, causing increased network traffic.
6.3.12 RESTRICTED GROUND FAULT
PATH: ACTUAL VALUES
METERING
RESTRICTED GROUND FAULT CURRENTS
RESTRICTED GROUND FAULT 1(6)
The differential and restraint current values for the restricted ground fault element are displayed in this menu.
MESSAGE
PMU 1 V2:
0.0000 kV, 0.00°
MESSAGE
PMU 1 V0:
0.0000 kV, 0.00°
Range: Substituted with zero if delta-connected VTs.
MESSAGE
PMU 1 IA:
0.0000 kA, 0.00°
MESSAGE
PMU 1 IB:
0.0000 kA, 0.00°
MESSAGE
PMU 1 IC:
0.0000 kA, 0.00°
MESSAGE
PMU 1 IG:
0.0000 kA, 0.00°
MESSAGE
PMU 1 I1:
0.0000 kA, 0.00°
MESSAGE
PMU 1 I2:
0.0000 kA, 0.00°
MESSAGE
PMU 1 I0:
0.0000 kA, 0.00°
MESSAGE
PMU 1 FREQUENCY:
0.0000 Hz
MESSAGE
PMU 1 df/dt:
0.0000 Hz/s
MESSAGE
PMU 1 CONFIG CHANGE
COUNTER: 0
Range: 0 to 65535
PMU AGGREGATOR 1
PMU AGGREGATOR 1
PDU SIZE: 0
RESTRICTED
GROUND FAULT 1
RGF 1 DIFF
Igd:
0.000
A
MESSAGE
RGF 1 RESTR Igr:
0.000
A
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...