5-252
F60 Feeder Protection System
GE Multilin
5.7 CONTROL ELEMENTS
5 SETTINGS
5
5.7.10 DIGITAL ELEMENTS
PATH: SETTINGS
CONTROL ELEMENTS
DIGITAL ELEMENTS
DIGITAL ELEMENT 1(48)
Digital elements run once per power system cycle.
As such they can easily fail to react to an input signal or a block signal with a duration less than one power system
cycle. This also means that digital element output can react up to one power system cycle later than the pickup and
reset delay settings indicate.
Do not use digital elements with transient signals, such as communications commands. Do not use digital elements
where random delays of up to one cycle cannot be tolerated, such as in high speed protection.
There are 48 identical digital elements available, numbered 1 to 48. A digital element can monitor any FlexLogic operand
and present a target message and/or enable events recording depending on the output operand state. The digital element
settings include a name which will be referenced in any target message, a blocking input from any selected FlexLogic oper-
and, and a timer for pickup and reset delays for the output operand.
•
DIGITAL ELEMENT 1 INPUT:
Selects a FlexLogic operand to be monitored by the digital element.
•
DIGITAL ELEMENT 1 PICKUP DELAY:
Sets the required time delay from element pickup to element operation. If a
pickup delay is not required, set to "0". To avoid nuisance alarms, set the delay greater than the operating time of the
breaker.
•
DIGITAL ELEMENT 1 RESET DELAY:
Sets the time delay to reset. If a reset delay is not required, set to “0”.
•
DIGITAL ELEMENT 1 PICKUP LED
: This setting enables or disabled the digital element pickup LED. When set to
“Disabled”, the operation of the pickup LED is blocked.
DIGITAL ELEMENT 1
DIGITAL ELEMENT 1
FUNCTION: Disabled
Range: Disabled, Enabled
MESSAGE
DIG ELEM 1 NAME:
Dig Element 1
Range: 16 alphanumeric characters
MESSAGE
DIG ELEM 1 INPUT:
Off
Range: FlexLogic operand
MESSAGE
DIG ELEM 1 PICKUP
DELAY: 0.000
s
Range: 0.000 to 999999.999 s in steps of 0.001
MESSAGE
DIG ELEM 1 RESET
DELAY: 0.000
s
Range: 0.000 to 999999.999 s in steps of 0.001
MESSAGE
DIG ELEMENT 1
PICKUP LED: Enabled
Range: Disabled, Enabled
MESSAGE
DIG ELEM 1 BLOCK:
Off
Range: FlexLogic operand
MESSAGE
DIGITAL ELEMENT 1
TARGET: Self-reset
Range: Self-reset, Latched, Disabled
MESSAGE
DIGITAL ELEMENT 1
EVENTS: Disabled
Range: Disabled, Enabled
NOTE
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...