207
Communication operation and setting
4
PA
R
A
M
E
T
E
R
S
4.19.6 Modbus-RTU communication specifications
(Pr. 331, Pr. 332, Pr. 334, Pr. 343, Pr. 539, Pr. 549)
(1) Communication specifications
The communication specifications are given below.
Using the Modbus-RTU communication protocol, communication operation or parameter setting can be
performed from the RS-485 terminals of the inverter.
Parameter
Number
Name
Initial
Value
Setting Range
Description
331
RS-485
communication
station number
0
0
Broadcast communication is selected.
1 to 247
Specifies the inverter station number.
Set the inverter station numbers when two or more
inverters are connected to one personal computer.
332
RS-485
communication
speed
96
3, 6, 12, 24, 48,
96, 192, 384
Set the communication speed.
The setting value
u
100 equals the communication speed.
For example, the communication speed is 9600bps when
the setting value is "96".
334
RS-485
communication parity
check selection
2
0
Without parity check
Stop bit length 2bits
1
With odd parity check
Stop bit length 1bit
2
With even parity check
Stop bit length 1bit
343
Communication error
count
0
Displays the number of communication errors during
Modbus-RTU communication. Reading only
539
Modbus-RTU
communication check
time interval
9999
0
Modbus-RTU communication can be made, but the inverter
will come to trip in the NET operation mode.
0.1 to 999.8s
Set the interval of communication check time.
(same specifications as
Pr. 122
)
9999
No communication check (signal loss detection)
549
Protocol selection
0
0
Mitsubishi inverter (computer link) protocol
1
Modbus-RTU protocol
The above parameters can be set when
Pr. 160 User group read selection
= "0".
(Refer to page 173)
CAUTION
When Modbus-RTU communication is performed from the master with address 0 (station 0) set, broadcast communication is
selected and the inverter does not send a response message to the master.
When response from the inverter is necessary, set a value other than "0" in
Pr. 331
.
Some functions are invalid for broadcast communication.
(Refer to page 209.)
REMARKS
When using the Modbus-RTU protocol, set
Pr. 549 Protocol selection
to "1".
When the communication option is fitted with
Pr. 550 NET mode operation command source selection
set to "9999" (initial value), the
command source (e.g. run command) from the RS-485 terminals is invalid.
(Refer to page 184)
Item
Description
Related
Parameters
Communication protocol
Modbus-RTU protocol
Pr. 549
Conforming standard
EIA-485 (RS-485)
Number of inverters connected
1: N (maximum 32 units), setting is 0 to 247 stations
Pr. 331
Communication speed
Can be selected from 300, 600, 1200, 2400, 4800, 9600, 19200 and 38400bps
Pr. 332
Control protocol
Asynchronous system
Communication method
Half-duplex system
Communication
specifications
Character system
Binary(fixed to 8 bits)
Start bit
1bit
Stop bit length
Select from the following three types
No parity, stop bit length 2 bits
Odd parity, stop bit length 1 bit
Even parity, stop bit length 1 bit
Pr. 334
Parity check
Error check
CRC code check
Terminator
Not used
Waiting time setting
Not used