3
Inverter and peripheral devices
1
OU
T
L
IN
E
1.2 Inverter and peripheral devices
CAUTION
· Do not install a power factor correction capacitor, surge suppressor or capacitor type filter on the inverter output side. This will
cause the inverter to trip or the capacitor, and surge suppressor to be damaged. If any of the above devices are connected,
immediately remove them.
· Electromagnetic wave interference
The input/output (main circuit) of the inverter includes high frequency components, which may interfere with the communication
devices (such as AM radios) used near the inverter. In this case, set the EMC filter valid to minimize interference.
(Refer topage 13.)
· Refer to the instruction manual of each option and peripheral devices for details of peripheral devices.
Power regeneration
common converter
(FR-CV
*1
)
Power regeneration
converter (MT-RC
*2
)
Resistor unit
(FR-BR
*1
, MT-BR5
*2
)
Brake unit
(FR-BU2, FR-BU
*1
, MT-BU5
*2
)
High power factor
converter
(FR-HC
*1
, MT-HC
*2
)
P/+
P/+
PR
PR
Programmable controller
Three-phase AC power supply
AC reactor
(FR-HAL)
DC reactor
(FR-HEL)
R/L1 S/L2 T/L3
P/+
N/-
P/+
P1
U V W
Moulded case circuit
breaker (MCCB)
or earth leakage circuit
breaker (ELB), fuse
Magnetic contactor(MC)
RS-485 terminal block
EMC filter
(ferrite core)
(FR-BSF01, FR-BLF)
Motor
Devices connected to the output
Use within the permissible power supply
specifications of the inverter.
The regeneration braking
capability of the inverter can be
exhibited fully.
Install this as required.
Install the magnetic contactor to ensure safety.
Do not use this magnetic contactor to start and
stop the inverter.
Doing so will cause the inverter life to be shorten.
The inverter can be
connected with computers
such as programmable
controller.
It supports Mitsubishi inverter
protocol and Modbus-RTU
(binary) protocol.
Do not install a power factor correction capacitor,
surge suppressor or EMC filter (capacitor) on the
output side of the inverter.
When installing a moulded case circuit breaker on the
output side of the inverter, contact each manufacturer
for selection of the moulded case circuit breaker.
Power supply harmonics
can be greatly suppressed.
Install this as required.
Greater braking capability
is obtained.
Install this as required.
The breaker must be selected carefully since
an in-rush current flows in the inverter at
power on.
Install an EMC filter (ferrite
core) to reduce the
electromagnetic noise
generated from the inverter.
Effective in the range from
about 1MHz to 10MHz.
A wire should be wound four
turns at a maximum.
Earth
Earth
To prevent an electric shock, always earth the
motor and inverter.
EMC filter
(ferrite core)
(FR-BLF)
The 01160 or less
has a built-in common
mode choke.
*1 Compatible with the 01160 or less.
*2 Compatible with the 01800 or more.
Earth
For the 01800 or more, a
DC reactor is supplied.
Always install the reactor.
Reactor (FR-HAL, FR-HEL)
Reactors (option) should be used when power
harmonics measures are taken, the power factor is
to be improved or the inverter is installed near a
large power supply system (1000kVA or more). The
inverter may be damaged if you do not use reactors.
Select the reactor according to the model.
For the 01160 or less, remove the jumpers across
terminals P/+-P1 to connect to the DC reactor.
(Refer to page 304)
(Refer to page 4)
(Refer to page 4)
(Refer to chapter 2 of page 4.)
I
nverter
(FR-F700)
The life of the inverter is influenced by surrounding air
temperature. The surrounding air temperature should be
as low as possible within the permissible range.
Especially when mounting the inverter inside an
enclosure, take cautions of the surrounding air
temperature.
(Refer to page 9)
Wrong wiring might lead to damage of the inverter. The
control signal lines must be kept fully away from the main
circuit to protect them from noise.
(Refer to page 12)
Refer to
page 13
for the built-in EMC filter.