215
Communication operation and setting
4
PA
R
A
M
E
T
E
R
S
(6) Modbus registers
z
System environment variable
*1
The communication parameter values are not cleared.
*2
For write, set the data as a control input instruction. For read, data is read as an inverter operating status.
*3
For write, set data as the operation mode setting. For read, data is read as the operation mode status.
z
Real-time monitor
Refer to
page 126
for details of the monitor description.
*1
Input terminal monitor details
*2
Output terminal monitor details
Register
Definition
Read/Write
Remarks
40002
Inverter reset
Write
Any value can be written
40003
Parameter clear
Write
Set H965A as a written value.
40004
All parameter clear
Write
Set H99AA as a written value.
40006
Parameter clear
*1
Write
Set H5A96 as a written value.
40007
All parameter clear
*1
Write
Set HAA99 as a written value.
40009
Inverter status/control input instruction
*2
Read/write
See below.
40010
Operation mode/inverter setting
*3
Read/write
See below.
40014
Running frequency (RAM value)
Read/write
According to the
Pr. 37
and
Pr. 144
settings, the
frequency and selectable speed are in 1r/min
increments.
40015
Running frequency (EEPROM value)
Write
b15
b0
CS
RES
STOP
MRS
JOG
RH
RM
RL
RT
AU
STR
STF
b15
b0
ABC2 ABC1
FU
OL
IPF
SU
RUN
*3
The setting depends on capacities. (01160 or less/01800 or more)
*4
When
Pr.37
= "1 to 9998" or
Pr. 144
= "2 to 10, 102 to 110," the unit is an integral value (one increment).
(Refer to page 125
)
<Inverter status/control input instruction>
*1
The signal within parentheses is the initial setting. The description changes depending on the setting of
Pr. 180 to Pr. 189 (input
terminal function selection) (page110)
.
Each assigned signal is valid or invalid depending on NET.
(Refer to page 184)
*2
The signal within parentheses is the initial setting. The description changes depending on the setting of
Pr. 190 to Pr. 196 (output
terminal function selection) (page116)
.
Bit
Definition
Control input instruction
Inverter status
0
Stop command
RUN (inverter running)
*2
1
Forward rotation command
Forward rotation
2
Reverse rotation command
Reverse rotation
3
RH (high speed operation command)
*1
SU (up to frequency)
*2
4
RM (middle speed operation command)
*1
OL (overload)
*2
5
RL (low speed operation command)
*1
IPF (instantaneous power failure)
*2
6
JOG (Jog operation)
*1
FU (frequency detection)
*2
7
RT (second function selection)
*1
ABC1 (fault)
*2
8
AU (current input selection)
*1
ABC2 (
)
*2
9
CS
(selection of automatic restart after
instantaneous power failure)
*1
0
10
MRS (output stop)
*1
0
11
STOP (start self-holding)
*1
0
12
RES (reset)
*1
0
13
0
0
14
0
0
15
0
Fault occurrence
<Operation mode/inverter setting>
The restrictions depending on the
operation mode changes according
to the computer link specifications.
Mode
Read
Value
Written
Value
EXT
H0000
H0010
PU
H0001
EXT
JOG
H0002
PU
JOG
H0003
NET
H0004
H0014
PU+
EXT
H0005
Register
Description
Increments
40201 Output frequency/Speed
*4
0.01Hz/1
40202 Output current
0.01A/0.1A
*3
40203 Output voltage
0.1V
40205
Frequency setting value/Speed
setting
*4
0.01Hz/1
40206 Running speed
1r/min
40208 Converter output voltage
0.1V
40209 Regenerative brake duty
0.1%
40210
Electronic thermal relay function
load factor
0.1%
40211
Output current peak value
0.01A/0.1A
*3
40212 Converter output voltage peak value
0.1V
40213 Input power
0.01kW/
0.1kW
*3
40214 Output power
0.01kW/
0.1kW
*3
40215 Input terminal status
*1
40216 Output terminal status
*2
40217 Load meter
0.1%
40220 Cumulative energization time
1h
40223 Actual operation time
1h
40224 Motor load factor
0.1%
40225 Cumulative power
1kWh
40250 Power saving effect
Variable
40251 Cumulative saving power
Variable
40252 PID set point
0.1%
40253 PID measured value
0.1%
40254 PID deviation
0.1%
Register
Description
Increments
Summary of Contents for F700