4
Inverter and peripheral devices
1.2.1
Peripheral devices
Check the inverter model of the inverter you purchased. Appropriate peripheral devices must be selected according
to the capacity. Refer to the following list and prepare appropriate peripheral devices:
400V class
Motor
Output
(kW)
*1
Applicable Inverter Model
Breaker Selection
*2
Input Side Magnetic
Contactor
*3
Without reactor
connection
With reactor
connection
Without reactor
connection
With reactor
connection
0.75
FR-F740-00023-EC
30AF 5A
30AF 5A
S-N10
S-N10
1.5
FR-F740-00038-EC
30AF 10A
30AF 10A
S-N10
S-N10
2.2
FR-F740-00052-EC
30AF 10A
30AF 10A
S-N10
S-N10
3.7
FR-F740-00083-EC
30AF 20A
30AF 15A
S-N10
S-N10
5.5
FR-F740-00126-EC
30AF 30A
30AF 20A
S-N20, S-N21
S-N11, S-N12
7.5
FR-F740-00170-EC
30AF 30A
30AF 30A
S-N20, S-N21
S-N20, S-N21
11
FR-F740-00250-EC
50AF 50A
50AF 40A
S-N20, S-N21
S-N20, S-N21
15
FR-F740-00310-EC
100AF 60A
50AF 50A
S-N25
S-N20, S-N21
18.5
FR-F740-00380-EC
100AF 75A
100AF 60A
S-N25
S-N25
22
FR-F740-00470-EC
100AF 100A
100AF 75A
S-N35
S-N25
30
FR-F740-00620-EC
225AF 125A
100AF 100A
S-N50
S-N50
37
FR-F740-00770-EC
225AF 150A
225AF 125A
S-N65
S-N50
45
FR-F740-00930-EC
225AF 175A
225AF 150A
S-N80
S-N65
55
FR-F740-01160-EC
225AF 200A
225AF 175A
S-N80
S-N80
75
FR-F740-01800-EC
225AF 225A
S-N95
90
FR-F740-01800-EC
225AF 225A
S-N150
110
FR-F740-02160-EC
225AF 225A
S-N180
132
FR-F740-02600-EC
400AF 400A
S-N220
160
FR-F740-03250-EC
400AF 400A
S-N300
185
FR-F740-03610-EC
400AF 400A
S-N300
220
FR-F740-04320-EC
600AF 500A
S-N400
250
FR-F740-04810-EC
600AF 600A
S-N600
280
FR-F740-05470-EC
600AF 600A
S-N600
315
FR-F740-06100-EC
800AF 700A
S-N600
355
FR-F740-06830-EC
800AF 800A
S-N600
400
FR-F740-07700-EC
1000AF 900A
S-N800
450
FR-F740-08660-EC
1000AF 1000A
1000A
Rated product
500
FR-F740-09620-EC
1200AF 1200A
1000A
Rated product
560
FR-F740-10940-EC
1600AF 1500A
1200A
Rated product
630
FR-F740-12120-EC
2000AF 2000A
1400A
Rated product
*1
Selections for use of the Mitsubishi 4-pole standard motor with power supply voltage of 400VAC 50Hz.
*2
Select the MCCB according to the power supply capacity.
Install one MCCB per inverter.
For using commercial-power supply operation, select a breaker with capacity which allows the motor to be
directly power supplied.
For the use in the United States or Canada, provide the appropriate UL and cUL listed Class RK5 or Class
L type fuse or UL 489 molded case circuit breaker (MCCB) that is suitable for branch circuit protection.
(Refer to the Installation Guideline.)
*3
Magnetic contactor is selected based on the AC-1 class. The electrical durability of magnetic contactor is 500,000 times. When the magnetic
contactor is used for emergency stop during motor driving, the electrical durability is 25 times.
When using the MC for emergency stop during motor driving or using on the motor side during commercial-power supply operation, select the
MC with class AC-3 rated current for the motor rated current.
CAUTION
When the inverter capacity is larger than the motor capacity, select an MCCB and a magnetic contactor according to the
inverter model and cable and reactor according to the motor output.
When the breaker on the inverter primary side trips, check for the wiring fault (short circuit), damage to internal parts of the
inverter, etc. Identify the cause of the trip, then remove the cause and power on the breaker.
MCCB
INV
MCCB
INV
IM
IM
Summary of Contents for F700
Page 327: ...318 MEMO ...
Page 340: ...331 MEMO ...