140
Operation selection at power failure
and instantaneous power failure
4.12.2 Power failure-time deceleration-to-stop function (Pr. 261 to Pr. 266 )
The above parameters can be set when
Pr. 160 User group read selection
= "0".
(Refer to page 173)
* When the setting of
Pr. 21 Acceleration/deceleration time increments
is "0" (initial value), the setting range is "0 to 3600s" and the setting increments are
"0.1s", and when the setting is "1", the setting range is "0 to 360s" and the setting increments are "0.01s"
When a power failure or undervoltage occurs, the inverter can be decelerated to a stop or can be decelerated
and re-accelerated to the set frequency.
Parameter
Number
Name
Initial
Value
Setting
Range
Description
261
Power failure stop
selection
0
Operation at
undervoltage or
power failure
At power restoration
during power failure
deceleration
Deceleration time to a
stop
0
Coasts to a stop
Coasts to a stop
—
1
Decelerates to a stop
Decelerates to a stop
Depends on
Pr. 262
to
Pr. 266
settings
2
Decelerates to a stop
Accelerates again
Depends on
Pr. 262
to
Pr. 266
settings
21
Decelerates to a stop
Decelerates to a stop
Automatically adjusts
the deceleration time
22
Decelerates to a stop
Accelerates again
Automatically adjusts
the deceleration time
262
Subtracted frequency
at deceleration start
3Hz
0 to 20Hz
Normally operation can be performed with the initial value unchanged. But
adjust the frequency according to the magnitude of the load specifications
(moment of inertia, torque).
263
Subtraction starting
frequency
50Hz
0 to
120Hz
When output frequency
t
Pr. 263
Decelerate from the speed obtained from output frequency minus
Pr. 262
.
When output frequency
Pr. 263
Decelerate from output frequency
9999
Decelerate from the speed obtained from output frequency minus
Pr. 262
.
264
Power-failure
deceleration time 1
5s
0 to 3600/
360s *
Set a deceleration slope down to the frequency set in
Pr. 266
.
265
Power-failure
deceleration time 2
9999
0 to 3600/
360s *
Set a deceleration slope below the frequency set in
Pr. 266
.
9999
Same slope as in
Pr. 264
266
Power failure
deceleration time
switchover frequency
50Hz
0 to
400Hz
Set the frequency at which the deceleration slope is switched from the
Pr. 264
setting to the
Pr. 265
setting.
(1) Connection and parameter setting
Remove the jumpers across terminals R/L1-R1/L11 and
across terminals S/L2-S1/L21, and connect terminals R1/
L11 and P/+ and terminals S1/L21 and N/-.
When setting of
Pr. 261
is not "0", the inverter decelerates to
a stop if an undervoltage, power failure or input phase loss
(when
Pr. 872
="1"(input phase loss enabled)) occurs.
(2) Operation outline of deceleration to stop at
power failure
If an undervoltage or power failure occurs, the output
frequency is dropped by the frequency set in
Pr. 262
.
Deceleration is made in the deceleration time set in
Pr. 264
.
(The deceleration time setting is the time required from
Pr. 20
Acceleration/deceleration reference frequency
to a stop.)
When the frequency is low and enough regenerative energy
is not provided, for example, the deceleration time (slope)
from
Pr. 265
to a stop can be changed.
Power supply
Remove the jumper
Inverter
S/L2
T/L3
S1/L21
P/+
N/
−
R1/L11
R/L1
Connect terminal
R1/L11 and P/+
and terminal
S1/L21 and N/-.
Pr.264
Power-failure
deceleration time 1
Pr.265
Power-failure
deceleration
time 2
Time
Power supply
Output
frequency
Subtracted
frequency at
deceleration start
Pr.262
Power-failure
deceleration
time switchover
frequency
Pr.266