161
Frequency setting by analog input (terminal 1, 2, 4)
4
PA
R
A
M
E
T
E
R
S
(2) Override function
(Pr. 252, Pr. 253)
4.16.3 Response level of analog input and noise elimination (Pr. 74)
The above parameters can be set when
Pr. 160 User group read selection
= "0".
(Refer to page 173)
Effective for eliminating noise in the frequency setting circuit.
Increase the filter time constant if steady operation cannot be performed due to noise. A larger setting results in
slower response. (The time constant can be set between approximately 10ms to 1s with the setting of 0 to 8.)
Override connection diagram
Use the override function to change the main speed at a fixed ratio.
Set any of "4, 5, 14, 15" in
Pr. 73
to select an override.
When an override is selected, the terminal 1 or terminal 4 is used for the main
speed setting and the terminal 2 for the override signal. (When the main speed of
the terminal 1 or terminal 4 is not input, compensation made by the terminal 2
becomes invalid.)
Using
Pr. 252
and
Pr. 253
, set the override range.
How to find the set frequency for override
Set frequency (Hz) = Main speed set frequency (Hz)
u
Main speed set frequency (Hz): Terminal 1, 4 input, multi-speed setting
Compensation amount (%): Terminal 2 input
Example)When
Pr. 73
= "5"
The set frequency changes as shown below according to the
terminal 1 (main speed) and terminal 2 (auxiliary) inputs.
CAUTION
When the
Pr. 73
setting was changed, check the voltage/current input switch setting. Different setting may cause a fault, failure
or malfunction. (
Refer to
page 155
for setting.)
REMARKS
The AU signal must be turned on to use the terminal 4.
When inputting compensation to multi-speed operation or remote setting, set "1" (compensation made) to
Pr. 28 Multi-speed
input compensation selection
. (Initial value is "0")
i
Parameters referred to
i
Pr. 28 Multi-speed input compensation selection
Refer to page 86
Pr. 73 Analog input selection
Refer to page 155
The time constant of the primary delay filter relative to external frequency command (analog input (terminal 1,
2, 4) signal) can be set.
Parameter
Number
Name
Initial Value
Setting Range
Description
74
Input filter time constant
1
0 to 8
Set the primary delay filter time
constant for the analog input. A
larger setting results in slower
response.
10
2
5
Forward
rotation
Main
speed
Inverter
STF
1
(-)
(+)
Override
setting
PC
Compensation amount (%)
100(%)
Pr.252
0V
2.5V
(5V)
5V
(10V)
0
50
100
150
200
Initial value
(50% to 150%)
Voltage across terminals 2-5
Pr.253
Override value (%)
0
2.5
5
0
Terminal 1 input voltage (V)
Set frequency (Hz)
Terminal 2 5VDC
input(150%)
Terminal 2 0V
input(50%)
Terminal 2 2.5VDC
input(100%)
25
12.5
50
37.5
75