274
Causes and corrective actions
(3) Alarm
When an alarm occurs, the output is not shut off. You can also output an alarm signal by making parameter
setting. (Set "98" in any of
Pr. 190 to Pr. 196 (output terminal function selection)
.
(Refer to page
116
.)
(4) Fault
When a fault occurs, the inverter trips and a fault signal is output.
Operation Panel
Indication
FN
FR-PU04
FR-PU07
FN
Name
Fan alarm
Description
For the inverter that contains a cooling fan,
appears on the operation panel when the cooling fan
stops due to a fault or different operation from the setting of
Pr. 244 Cooling fan operation selection
.
Check point
Check the cooling fan for an alarm.
Corrective action
Check for fan failure. Please contact your sales representative.
Operation Panel
Indication
E.OC1
FR-PU04
FR-PU07
OC During Acc
Name
Overcurrent trip during acceleration
Description
When the inverter output current reaches or exceeds approximately 170% of the rated current during
acceleration, the protective circuit is activated to stop the inverter output.
Check point
1. Check for sudden acceleration.
2. Check that the downward acceleration time is not long in vertical lift application.
3. Check for output short circuit.
4. Check that stall prevention operation is correct.
5. Check that the regeneration is not performed frequently. (Check that the output voltage becomes
larger than the V/F reference voltage at regeneration and overcurrent occurs due to the high
voltage.)
Corrective action
1. Increase the acceleration time.
(Shorten the downward acceleration time in vertical lift application.)
2. When "E.OC1" is always lit at starting, disconnect the motor once and start the inverter.
If "E.OC1" is still lit, contact your sales representative.
3. Check the wiring to make sure that output short circuit does not occur.
4. Perform a correct stall prevention operation.
(Refer to
page 70.)
5. Set base voltage (rated voltage of the motor, etc.) in
Pr. 19 Base frequency voltage
.
(Refer to
page
78.)
Operation Panel
Indication
E.OC2
FR-PU04
FR-PU07
Stedy Spd OC
Name
Overcurrent trip during constant speed
Description
When the inverter output current reaches or exceeds approximately 170% of the rated current during
constant speed operation, the protective circuit is activated to stop the inverter output.
Check point
1. Check for sudden load change.
2. Check for output short circuit.
3. Check that stall prevention operation is correct.
Corrective action
1. Keep load stable.
2. Check the wiring to avoid output short circuit.
3. Check that stall prevention operation setting is correct.
(Refer to
page 70.)
Operation Panel
Indication
E.OC3
FR-PU04
FR-PU07
OC During Dec
Name
Overcurrent trip during deceleration or stop
Description
When the inverter output current reaches or exceeds approximately 170% of the rated inverter current
during deceleration (other than acceleration or constant speed), the protective circuit is activated to
stop the inverter output.
Check point
1. Check for sudden speed reduction.
2. Check for output short circuit.
3. Check for too fast operation of the motor's mechanical brake.
4. Check that stall prevention operation setting is correct.
Corrective action
1. Increase the deceleration time.
2. Check the wiring to avoid output short circuit.
3. Check the mechanical brake operation.
4. Check that stall prevention operation setting is correct.
(Refer to
page 70.)
Summary of Contents for F700
Page 327: ...318 MEMO ...
Page 340: ...331 MEMO ...