4.17 Misoperation prevention and parameter setting restriction
4.17.1 Reset selection/disconnected PU detection/PU stop selection (Pr. 75)
Purpose
Parameter that must be Set
Refer to
Page
Limit reset function
Trips stop when PU is disconnected
Stop from PU
Reset selection/disconnected
PU detection/PU stop selection
Pr. 75
169
Prevention of parameter rewrite
Parameter write selection
Pr. 77
172
Prevention of reverse rotation of the
motor
Reverse rotation prevention
selection
Pr. 78
173
Display necessary parameters
Display of applied parameters
and user group function
Pr. 160, Pr. 172 to Pr. 174
173
Control of parameter write by
communication
EEPROM write selection
Pr. 342
195
You can select the reset input acceptance, disconnected PU (FR-DU07/FR-PU04/FR-PU07) connector detection
function and PU stop function.
Parameter
Number
Name
Initial
Value
Setting Range
Description
75
Reset selection/disconnected
PU detection/PU stop selection
14
01160 or
less
0 to 3, 14 to 17
For the initial value, reset always enabled,
without disconnected PU detection, and
with PU stop function are set.
01800 or
more
0 to 3, 14 to 17,
100 to 103,
114 to117
The above parameters can be set when
Pr. 160 User group read selection
= "0".
(Refer to page 173)
The
Pr. 75
value can be set any time. Also, if parameter (all) clear is executed, this setting will not return to the initial value.
Pr. 75
Setting
Reset Selection
Disconnected PU
Detection
PU Stop Selection
Reset Limit
(01800 or more)
0
Reset input always enabled
If the PU is disconnected,
operation will be continued.
Pressing
decelerates
the motor to a stop only in
the PU operation mode.
Not function
1
Reset input enabled only when the
inverter trips
2
Reset input always enabled
When the PU is
disconnected, the inverter
trips.
3
Reset input enabled only when the
inverter trips
14
(initial
value)
Reset input always enabled
If the PU is disconnected,
operation will be continued.
Pressing
decelerates
the motor to a stop in any of
the PU, external and
communication operation
modes.
15
Reset input enabled only when the
inverter trips
16
Reset input always enabled
When the PU is
disconnected, the inverter
trips.
17
Reset input enabled only when the
inverter trips
100
Reset input always enabled
If the PU is disconnected,
operation will be continued.
Pressing
decelerates
the motor to a stop only in
the PU operation mode.
Function
101
Reset input enabled only when the
inverter trips
102
Reset input always enabled
When the PU is
disconnected, the inverter
trips.
103
Reset input enabled only when the
inverter trips
114
Reset input always enabled
If the PU is disconnected,
operation will be continued.
Pressing
decelerates
the motor to a stop in any of
the PU, external and
communication operation
modes.
115
Reset input enabled only when the
inverter trips
116
Reset input always enabled
When the PU is
disconnected, the inverter
trips.
117
Reset input enabled only when the
inverter trips