Special operation and frequency control
4.20.5 Regeneration avoidance function (Pr. 882 to Pr. 886)
(1) What is regeneration avoidance function?
(Pr. 882, Pr. 883)
When the regeneration status is serious, the DC bus voltage rises and an overvoltage fault (E. OV
) may occur.
When this bus voltage rise is detected and the bus voltage level reaches or exceeds
Pr. 883
, increasing the
frequency avoids the regeneration status.
The regeneration avoidance operation, you can select whether it is always activated or activated only a constant
speed.
Setting
Pr. 882
to "1, 2" validates the regeneration avoidance function.
This function detects a regeneration status and increases the frequency to avoid the regeneration status.
z
Possible to avoid regeneration by automatically increasing the frequency and continue operation if the fan
happens to rotate faster than the set speed due to the effect of another fan in the same duct.
Parameter
Number
Name
Initial
Value
Setting
Range
Description
882
Regeneration
avoidance operation
selection
0
0
Regeneration avoidance function invalid
1
Regeneration avoidance function valid
2
Regeneration avoidance function is valid only during a constant
speed operation
883
Regeneration
avoidance operation
level
760VDC/
785VDC *
300 to 800V
Set the bus voltage level at which regeneration avoidance
operates. When the bus voltage level is set to low, overvoltage
error will be less apt to occur. However, the actual deceleration
time increases. The set value must be higher than the power
supply voltage
u
.
* The initial value differs according to the inverter capacity.
(01160 or less/01800 or more)
884
Regeneration
avoidance at
deceleration
detection sensitivity
0
0
Regeneration avoidance by bus voltage change ratio is invalid
1 to 5
Set sensitivity to detect the bus voltage change ratio
Setting
1
5
Detection sensitivity low
high
885
Regeneration
avoidance
compensation
frequency limit value
6Hz
0 to 10Hz
Set the limit value of frequency which rises at activation of
regeneration avoidance function.
9999
Frequency limit invalid
886
Regeneration
avoidance voltage
gain
100%
0 to 200%
Adjusts responsiveness at activation of regeneration avoidance.
A larger setting will improve responsiveness to the bus voltage
change. However, the output frequency could become unstable.
The above parameters can be set when
Pr. 160 User group read selection
= "0".
(Refer to page 173)
REMARKS
The inclination of the frequency increased or decreased by the regeneration avoidance function changes depending on the
regeneration status.
The DC bus voltage of the inverter is normally about
times greater than the input voltage.
When the input voltage is 440VAC, the bus voltage is about 622VDC.
However, it varies with the input power waveform.
The
Pr. 883
setting should be kept higher than the DC bus voltage level. Otherwise, the regeneration avoidance function is always on
even in the non-regeneraion status and the frequency increases.
While overvoltage stall (
) is activated only during deceleration and stops the decrease in output frequency, the regeneration
avoidance function is always on (
Pr. 882
= 1) or activated only during a constant speed (
Pr. 882
= 2) and increases the frequency
according to the regeneration amount.
Note that when coping parameters to the inverter without this function (inverter assembled in and before September 2005),
copied
Pr.882
="2" is regarded as
Pr.882
="0"(regeneration avoidance function invalid).
2
Pr.883
Time
Time
Regeneration avoidance operation
example for acceleration
Bus voltage
(VDC)
Output
frequency(Hz)
During regeneration
avoidance function operation
Pr.883
Time
Time
Regeneration avoidance operation
example for constant speed
Bus voltage
(VDC)
Output
frequency(Hz)
During regeneration
avoidance function operation
Pr.883
Time
Time
Bus voltage
(VDC)
Output
frequency(Hz)
During regeneration
avoidance function operation
Regeneration avoidance operation
example for deceleration
2