F08 Installation & Programming Manual
Document No: LT0082
Application Considerations
Page 5-8
24 March 2006
Issue 3.04
DETECTOR
GAS GROUP 11A OR 11B
GAS GROUP 11C
CCT LENGTH
CCT LENGTH
TYPE NBR BASE NBR 1.0mm
2
0.75mm
2
NBR 1.0mm
2
0.75mm
2
FLAME
MS302Ex
M300
40(m)
1.5km(R)
1.1km(R)
40(m)
0.7km (C)
0.7km (C)
(50
Ω
) (50
Ω
)
(70nF)
(70nF)
30
0.85km (C)
0.85km (C)
(85nF)
(85nF)
20
1km (C)
1km (C)
(100nF)
(100nF)
10
1.15km (C)
1.1km (R)
(115nF)
(50
Ω
)
1
1.28km (C)
1.1km (R)
(128nF)
(50
Ω
)
SMOKE C29BEx Z94C 40(m) 1.5km
(R) 1.1km (R)
40(m)
0.9km (C)
0.9KM (C)
(50
Ω
) (50
Ω
)
(90nF)
(90nF)
30
1km (C)
1km (C)
(100nF)
(100nF)
20
1.1km (C)
1.1km (C)
(110nF)
(110nF)
10
1.2km (C)
1.1km (R)
(120nF)
(50
Ω
)
1
1.29km (C)
1.1km (R)
(129nF)
(50
Ω
)
FLAME
R24BEx
-
5(m)
1.5km (R)
1.1km (R)
2(m)
1.13km (C)
1.1km (R)
(50
Ω
) (50
Ω
)
(113nF)
(50
Ω
)
1
1.2km (C)
1.1km (R)
(120nF)
(50
Ω
)
HEAT FW105
-
-
NOTE NOTE
-
1.3km 1.1km
(R)
2 & 3
2 & 3
TOT
(50
Ω
) (50
Ω
)
(130nF)
(50
Ω
)
HEAT
T54B
-
40(m)
1.5km (R)
1.1km (R)
40(m)
1.3km (C)
1.1km (R)
(50
Ω
) (50
Ω
)
(130nF)
(50
Ω
)
HEAT
T56B
Z500N
40(m)
1.5km (R)
1.1km (R)
40(m)
1.3km (C)
1.1km (R)
(50
Ω
) (50
Ω
)
(130nF)
(50
Ω
)
Table 5.2.3
Maximum Detector Quantity & Cable Length for KFDO-CS-Ex 1.51P/2.51P
1.
If the circuit length is limited due to capacitance or inductance, (e.g. 1.3km (C)), then
the difference in cable length to that limited by resistance can be used on the non-
hazardous side. I.e. circuit length is from the isolating repeater to the EOL when the
length is limited due to cable capacitance/inductance, or from the F08's terminal
through the isolating repeater to the EOL when the limit to due to resistance.
2.
Cable resistance shown is for the complete circuit, i.e. both cables in the pair. The
value of 34
Ω
per km (return) is used for 1mm
2
.
3.
The maximum resistances shown for the fire wire circuits must include both cable and
fire wire (see Table 5.2.2 and associated Note 2).
4.
The letter in ( ) after the cable length, and the value in ( ) under the cable length
specify which parameter out of capacitance (C), inductance (L), and resistance (R)
provides the limitation, and what the limiting value is.
5.
The (m) after a detector quantity indicates the maximum quantity allowed per circuit.
Summary of Contents for F08