F08 Installation & Programming Manual
Document No: LT0082
Appendix A2 - Compatible Actuating Devices
DETECTORS CERTIFIED WITH THE F08 FOR
HAZARDOUS AREA APPLICATIONS
MAX NO. OF
DETECTORS
TYPE
DESCRIPTION
Iq uA
PER ZONE
C29BEx
# Ionisation Smoke Detector Z94C Base
45
40
R24BEx
# Dual Spectrum InfraRed Flame Detector
250
5
T54B
Probe Type E Heat Detector
0
40
T56B
# Heat Detector Types A, B, C, D Z500N Base
0
40
MS302Ex
# IS InfraRed Flame Detector
100
40
-
Short Circuit Device
-
40
With Pepperl & Fuchs KFDO-CS-Ex 1.51P (or 2.51P) Isolating Repeater.
# F08 Input type must be programmed as Type 1 or Type 4.
OLSEN RANGE
MAX
NUMBER
TYPE
DESCRIPTION
Iq uA
WITH EOL
B111B
Beam Type Smoke Detector
0
40
T54B
Probe Type E Heat Detector
0
40
V41B
Ultraviolet Flame Detector
0
40
V42B
Ultraviolet Flame Detector
0
40
FW81B
Heat Detector Cable
0
1000m
SIMPLEX RANGE
MAX
NUMBER
TYPE
DESCRIPTION
Iq uA
WITH EOL
4098-9601EA
Photoelectric Smoke Detector
100
40
4098-9603EA
Ionisation Smoke Detector
100
40
4098-9618EA
Heat Detector Type A
100
40
4098-9619EA
Heat Detector Type B
100
40
4098-9621EA
Heat Detector Type D
100
40
All with 4098-9788EA Base
SYSTEM SENSOR RANGE
MAX
NUMBER
TYPE
DESCRIPTION
Iq uA
WITH EOL
885WP-B ^ % Weatherproof Heat Detector Type B
50
40
NOTES
1)
The maximum number of detectors per AZF/AZC allowed by code is 40.
2)
Not all detectors listed are approved to the appropriate Australian Standard.
3)
For use in HAZARDOUS AREAS, the listed Intrinsically Safe (IS) detectors must be
used in conjunction with the listed isolating repeaters, or flame proof detectors be
used with flame proof wiring.
4)
Detectors indicated by a
“*”
are not current models and should not be used for new
installations.
Page A2-2
24 March 2006
Issue 3.04