Programming
4.11
EXIT PROGRAMMING CHECKLIST
The following checks are required to ensure that the system is correctly programmed and
configured.
1)
All zones toggled between DISABLED and ENABLED are ISOLATED upon exit from
the programming mode. They will need to be DE-ISOLATED before they are fully
operational.
2)
If the Ancillary Relay Supervision is toggled between DISABLED and ENABLED it
will be isolated upon exit from programming mode. It will need to be DE-ISOLATED
before use.
3)
Check that there are no Faults or Alarms indicated.
4)
Select each zone and perform a ZONE TEST.
-
Remember to manually ISOLATE or disconnect any zone "AUXILIARY
OUTPUT" control during the test if necessary.
-
Remember NON-LATCHING zones will not keep the "FLT" LED ON after the
"SILENCE" key is pressed.
-
Remember time delays are active during alarm test. Check that they
correspond to what is required.
5)
Select "ANCIL RELAY" and perform an output mapping test.
-
Mapped zones will be indicated by the zone "ALM" LED being ON.
-
Check operation of Relay Output.
6)
Select "MASTER ALARM" and perform an output mapping test.
-
Mapped zones will be indicated by the zone "ALM" LED being ON.
7)
Select "ALARM BELLS" and perform an output mapping test.
-
Mapped zones will be indicated by the zone "ALM" LED being ON.
-
Check operation of Bells Output.
8)
If the Ancillary Relay Supervision is enabled, disconnect one of the output wires and
check that a FAULT is registered.
9)
Finally; perform a System Test.