F08 Installation & Programming Manual
Document No: LT0082
Placing into Operation
3.3
POWER
UP
To place a correctly installed and programmed F08 FIP into operation perform the following
steps:
STEP 1
:
Ensure that the Mains Isolate Switch is OFF and that 240VAC is
available to the panel from the mains distribution switchboard.
STEP 2
:
Disconnect or physically isolate any outputs that must not be activated
as a result of an alarm or fault during commissioning. Eg Fire Brigade,
Alarm Bells or Suppression System.
STEP 3
:
Turn the Mains Isolate Switch ON.
STEP 4
:
Check that the green "MAINS ON" LED indicator is illuminated and all
other LED indicators are OFF.
STEP 5
:
Perform a System Test.
(a)
With the FIP in GLOBAL mode (all "SEL" LED indicators OFF)
Press the key once.
(b)
The amber "ISO" LED indicators for Ancillary Relay, Master Alarm and Alarm
Bells will illuminate.
TEST
(c)
After 5 seconds all LED indicators will illuminate and the internal sounder will
produce a steady tone for a period of 2 seconds.
(d)
A fault test will be carried out on each enabled and non-isolated zone,
stepping through zones by illuminating the "SEL" and "FLT" LED indicators.
(e)
An alarm test will be carried out on each enabled and non-isolated zone,
stepping through zones by illuminating "SEL" and "ALM" LED indicators.
(f)
All indicators turn off. (Except MAINS ON)
(g)
If a zone fault or alarm occurs during the test or the test fails, then check the
AZC connections.
STEP 6
:
Install and connect the batteries.
Page 3-4