5-68
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
PRODUCT SETUP
CHAPTER 5: SETTINGS
5
TxGOOSE1 ETYPE APPID
Range: 0 to 65535 in steps of 1
Default: 0
The value entered sets the APPID value in published GOOSE messages and can be used by subscribers to discriminate
TxGOOSE1 messages from other GOOSE messages.
The standard reserves the value range 0 to 16383 for GOOSE Type 1 (Fast messages), and reserves the value range
32768 to 41151 for GOOSE Type 1A (Trip messages). Some subscribers can process messages in the Type 1A range
faster than messages in the Type 1 range. The standard reserves the default value (0) to indicate lack of configuration.
The standard strongly recommends unique, source-orientated APPIDs within a given system.
TxGOOSE1 CONFREV
Range: 0 to 4294967295 in steps of 1
Default: 1
The entered value sets the confRev value in published GOOSE messages and can be used by subscribers to discriminate
TxGOOSE messages of the expected configuration revision from messages of a different revision. The standard requires
that CONFREV be incremented each time the members or the order of the members published is changed. The standard
states that the value of 0 is reserved.
TxGOOSE1 RETRANS TIME
Range: 0 to 100 ms in steps of 1 ms
Default: 4 ms
If the entered time is non-zero, when a member value change is detected, four event transmissions are sent, then
heartbeat transmissions resume. The interval between the first and second event transmissions, and between the
second and third, is the time set here. The interval between the third and the fourth event transmission is double the set
time. If the entered time is zero, only a single event transmission occurs, then heartbeat transmissions resume.
TxGOOSE1 TIME TO LIVE
Range: 1 to 300 s in steps of 1 s
Default: 300 s
The value entered sets the timeAllowedtoLive value in published TxGOOSE1 messages. The standard requires
subscribers to assume a failure has occurred when another TxGOOSE1 message is not received within the published
timeAllowedtoLive time.
Base this setting on the
TxGOOSE UPDATE TIME
and the tolerable number of contiguous message delivery misses. For
example, if the heartbeat time is 10 s, and missing up to three successive messages is tolerable, make the setting
10 * 3 + 1 = 31 s. The extra second is to ensure that arrival of the third heartbeat transmission beats the
timeAllowedtoLive timer.
TxGOOSE1 UPDATE TIME
Range: 1 to 60 s in steps of 1 s
Default: 60 s
This setting specifies the time interval between heartbeat messages, meaning messages that are sent periodically while
no events are detected.
TxGOOSE1 PORT ASSIGNMENT
Range: Disabled, Port-1; Port-2; Port-3; Ports-1,2; Ports-2,3; Ports-1,3; Ports-1,2,3
Default: Ports-1, 2, 3
This setting specifies the Ethernet ports for transmission of TxGOOSE1. When set to disabled, TxGOOSE1 messages are
not transmitted on any port no matter the state of GoEna. When set to Port-1, TxGOOSE1 is published over Ethernet
Port-1 only; while selecting Ports-1, 3 option, the same TxGOOSE1 is published to both Ports 1 and 3; and similarly if set
to Ports-1, 2, 3, all ports publish TxGOOSE1.
When setting
PRT2 REDUNDANCY
to Failover or to PRP, the TxGOOSE 1 port assignment needs to be set to ports 2
and 3 (Ports-2,3).
Also, Port 3 configuration in the CID file is ignored. The Port 3 ConnectedAP elements has no meaning, as ports 2
and 3 use the port 2 MAC address, IP address, and mask.