CHAPTER 5: SETTINGS
FLEXLOGIC
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
5-211
5
ELEMENT:
VTFF (Voltage
transformer fuse
failure)
SRC1 VT FF OP
SRC1 VT FF DPO
SRC1 VT FF VOL LOSS
SRC1 VT FF ALARM
Source 1 VT fuse failure detector has operated
Source 1 VT fuse failure detector has dropped out
Source 1 has lost voltage signals (V2 below 10% and V1 below 5% of nominal)
Source 1 has triggered a VT fuse failure alarm
SRC1 VT NEU WIRE OPEN
Source 1 VT neutral wire open detected. When the VT is connected in Delta,
do not enable this function because there is no neutral wire for Delta
connected VT.
SRC2 VT FUSE FAIL to SRC6
Same set of operands as shown for SRC1 VT FF
ELEMENT:
Disconnect switch
SWITCH 1 OFF CMD
SWITCH 1 ON CMD
SWITCH 1 CLOSED
SWITCH 1 OPEN
SWITCH 1 DISCREP
SWITCH 1 TROUBLE
SWITCH 1
Φ
A CLSD
SWITCH 1
Φ
A OPEN
SWITCH 1
Φ
A BAD ST
SWITCH 1
Φ
A INTERM
SWITCH 1
Φ
B CLSD
SWITCH 1
Φ
B OPEN
SWITCH 1
Φ
B BAD ST
SWITCH 1
Φ
B INTERM
SWITCH 1
Φ
C CLSD
SWITCH 1
Φ
C OPEN
SWITCH 1
Φ
C BAD ST
SWITCH 1
Φ
C INTERM
SWITCH 1 BAD STATUS
SWITCH 1 TAG ON
SWITCH 1 TAG OFF
SWITCH 1 SUBD CLSD
SWITCH 1 SUBD OPEN
SWITCH 1 BYPASS ON
SWITCH 1 BYPASS OFF
Disconnect switch 1 open command initiated
Disconnect switch 1 close command initiated
Disconnect switch 1 is closed
Disconnect switch 1 is open
Disconnect switch 1 has discrepancy
Disconnect switch 1 trouble alarm
Disconnect switch 1 phase A is closed
Disconnect switch 1 phase A is open
Disconnect switch 1 phase A bad status is detected (discrepancy between
the 89/a and 89/b contacts)
Disconnect switch 1 phase A intermediate status is detected (transition from
one position to another)
Disconnect switch 1 phase B is closed
Disconnect switch 1 phase B is open
Disconnect switch 1 phase B bad status is detected (discrepancy between
the 89/a and 89/b contacts)
Disconnect switch 1 phase B intermediate status is detected (transition from
one position to another)
Disconnect switch 1 phase C is closed
Disconnect switch 1 phase C is open
Disconnect switch 1 phase C bad status is detected (discrepancy between
the 89/a and 89/b contacts)
Disconnect switch 1 phase C intermediate status is detected (transition from
one position to another)
Disconnect switch 1 bad status is detected on any pole
Switch 1 tagged so manual trip and close is blocked
Switch 1 not tagged
Switch 1 status manually substituted to closed
Switch 1 status manually substituted to open
Switch 1 control interlocking is bypassed manually
Switch 1 control interlocking is not bypassed manually
SWITCH 2 to 24
Same set of operands as shown for SWITCH 1
ELEMENT:
Teleprotection
channel tests
TELEPRO CH1 FAIL
TELEPRO CH2 FAIL
TELEPRO CH1 ID FAIL
TELEPRO CH2 ID FAIL
TELEPRO CH1 CRC FAIL
TELEPRO CH2 CRC FAIL
TELEPRO CH1 PKT LOST
TELEPRO CH2 PKT LOST
Channel 1 failed
Channel 2 failed
The ID check for a peer relay on channel 1 has failed
The ID check for a peer relay on channel 2 has failed
CRC detected packet corruption on channel 1
CRC detected packet corruption on channel 2
CRC detected lost packet on channel 1
CRC detected lost packet on channel 2
ELEMENT:
Teleprotection
inputs/outputs
TELEPRO INPUT 1-1 On
↓
TELEPRO INPUT 1-16 On
TELEPRO INPUT 2-1 On
↓
TELEPRO INPUT 2-16 On
Flag is set, Logic =1
↓
Flag is set, Logic =1
Flag is set, Logic =1
↓
Flag is set, Logic =1
ELEMENT:
Thermal overload
protection
THERMAL PROT 1 PKP
THERMAL PROT 1 OP
Thermal overload protection 1 picked up
Thermal overload protection 1 operated
THERMAL PROT 2
Same set of operands as shown for THERMAL PROT 1
ELEMENT:
Trip bus
TRIP BUS 1 PKP
TRIP BUS 1 OP
Asserted when the trip bus 1 element picks up
Asserted when the trip bus 1 element operates
TRIP BUS 2 to 6
Same set of operands as shown for TRIP BUS 1
ELEMENT:
Underfrequency
UNDERFREQ 1 PKP
UNDERFREQ 1 OP
UNDERFREQ 1 DPO
Underfrequency 1 has picked up
Underfrequency 1 has operated
Underfrequency 1 has dropped out
Operand type
Operand syntax
Operand description