5-140
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
PRODUCT SETUP
CHAPTER 5: SETTINGS
5
Slow EGD exchanges (500 to 1000 ms) are generally used for the transfer and display of data items. The settings for the
fast and slow exchanges are as follows.
EXCH 1 DESTINATION
— This setting specifies the destination IP address of the produced EGD exchange. This is usually
unicast or broadcast.
EXCH 1 DATA RATE
— This setting specifies the rate at which this EGD exchange is transmitted. If the setting is 50 ms, the
exchange data is updated and sent once every 50 ms. If the setting is 1000 ms, the exchange data is updated and sent
once per second. EGD exchange 1 has a setting range of 50 to 1000 ms. Exchanges 2 and 3 have a setting range of 500 to
1000 ms.
EXCH 1 DATA ITEM 1 to 20/50
— These settings specify the data items that are part of this EGD exchange. Almost any data
from the F35 memory map can be configured to be included in an EGD exchange. The settings are the starting Modbus
register address for the data item in decimal format. See the Modbus memory map in the UR Series Communications
Guide for details. The Modbus memory map display shows addresses in hexadecimal format. Convert these hex values to
decimal format before entering them as values for these setpoints.
To select a data item to be part of an exchange, it is only necessary to choose the starting Modbus address of the item.
That is, for items occupying more than one Modbus register (for example, 32 bit integers and floating point values), only the
first Modbus address is required. The EGD exchange configured with these settings contains the data items up to the first
setting that contains a Modbus address with no data, or 0. That is, if the first three settings contain valid Modbus addresses
and the fourth is 0, the produced EGD exchange contains three data items.
5.3.5.17 IEC 60870-5-103 protocol
SETTINGS
PRODUCT SETUP
COMMUNICATIONS
IEC 60870-5-103
IEC 60870-5-103 is a companion standard to the IEC 60870-5 suite of standards for transmission protocols. It defines
messages and procedures for interoperability between protection equipment and devices of a control system in a
substation for communicating on a serial line.
The IEC 60870-5-103 protocol is enabled when the
SETTINGS
PRODUCT SETUP
COMMUNICATIONS
PROTOCOL
setting
is set to IEC 60870-5-103.
The IEC 60870-5-103 is an unbalanced (master-slave) protocol for coded-bit serial communication, exchanging
information with a control system. In the context of this protocol, the protection equipment is the slave and the control
system is the master. The communication is based on a point-to-point principle. The master must be able to interpret the
IEC 60870-5-103 communication messages.
EXCH 1 DATA ITEM 1:
0
Range: 0 to 65535 in steps of 1 (Modbus register
address range)
EXCH 1 DATA ITEM 50:
0
Range: 0 to 65535 in steps of 1 (Modbus register
address range)
IEC103
PROTOCOL
IEC103 COMMON
ADDRESS OF ASDU: 0
Range: 0 to 254 in steps of 1
IEC103 SYNC TIMEOUT:
1
Range: 1 to 1440 min in steps of 1
IEC103 INPUTS
BINARY
See below
IEC103 INPUTS
MEASURANDS
See below
IEC103 COMMANDS
See below
The F35 is provided with optional IEC 60870-5-103 communications capability. This feature is specified as a
software option at the time of ordering. See the Order Codes section in chapter 2 for details.