5-324
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
TRANSDUCER INPUTS/OUTPUTS
CHAPTER 5: SETTINGS
5
Table 5-35: RTD temperature vs. resistance
5.10.3 DCmA outputs
SETTINGS
TRANSDUCER I/O
DCMA OUTPUTS
DCMA OUTPUT H1(W8)
Temperature
Resistance (in ohms)
°C
°F
100
Ω
Pt
(DIN 43760)
120
Ω
Ni
100
Ω
Ni
10
Ω
Cu
–50
–58
80.31
86.17
71.81
7.10
–40
–40
84.27
92.76
77.30
7.49
–30
–22
88.22
99.41
82.84
7.88
–20
–4
92.16
106.15
88.45
8.26
–10
14
96.09
113.00
94.17
8.65
0
32
100.00
120.00
100.00
9.04
10
50
103.90
127.17
105.97
9.42
20
68
107.79
134.52
112.10
9.81
30
86
111.67
142.06
118.38
10.19
40
104
115.54
149.79
124.82
10.58
50
122
119.39
157.74
131.45
10.97
60
140
123.24
165.90
138.25
11.35
70
158
127.07
174.25
145.20
11.74
80
176
130.89
182.84
152.37
12.12
90
194
134.70
191.64
159.70
12.51
100
212
138.50
200.64
167.20
12.90
110
230
142.29
209.85
174.87
13.28
120
248
146.06
219.29
182.75
13.67
130
266
149.82
228.96
190.80
14.06
140
284
153.58
238.85
199.04
14.44
150
302
157.32
248.95
207.45
14.83
160
320
161.04
259.30
216.08
15.22
170
338
164.76
269.91
224.92
15.61
180
356
168.47
280.77
233.97
16.00
190
374
172.46
291.96
243.30
16.39
200
392
175.84
303.46
252.88
16.78
210
410
179.51
315.31
262.76
17.17
220
428
183.17
327.54
272.94
17.56
230
446
186.82
340.14
283.45
17.95
240
464
190.45
353.14
294.28
18.34
250
482
194.08
366.53
305.44
18.73
DCMA OUTPUT H1
DCMA OUTPUT H1
SOURCE: Off
Range: Off, any analog actual value parameter
DCMA OUTPUT H1
RANGE: –1 to 1 mA
Range: –1 to 1 mA, 0 to 1 mA, 4 to 20 mA
DCMA OUTPUT H1
MIN VAL: 0.000 pu
Range: –90.000 to 90.000 pu in steps of 0.001
DCMA OUTPUT H1
MAX VAL: 1.000 pu
Range: –90.000 to 90.000 pu in steps of 0.001