F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
GROUPED ELEMENTS
CHAPTER 5: SETTINGS
5
The positive-sequence restraint must be considered when testing for pickup accuracy and response time (multiple of
pickup). The operating quantity depends on how test currents are injected into the relay (single-phase injection):
Eq. 5-17
NEUTRAL IOC1 FUNCTION
— This setting enables and disables the neutral instantaneous overcurrent protection element.
NEUTRAL IOC1 SIGNAL SOURCE
— This setting selects the signal source for the neutral instantaneous overcurrent protection
element.
NEUTRAL IOC1 PICKUP
— This setting specifies the neutral instantaneous overcurrent pickup level in per-unit values.
NEUTRAL IOC1 PICKUP DELAY
— This setting delays the assertion of the
NEUTRAL IOC OP
operands. It is used to achieve timing
coordination with other elements and relays.
NEUTRAL IOC1 RESET DELAY
— This setting specifies a delay for the reset of the neutral instantaneous overcurrent element
between the operate output state and the return to logic 0 after the input passes outside the defined pickup range. This
setting is used to ensure that the relay output contacts are closed long enough to ensure reception by downstream
equipment.a
NEUTRAL IOC1 BLOCK
— Assertion of the operand assigned to this setting blocks operation of the neutral instantaneous
overcurrent element.
NEUTRAL IOC1 EVENTS
— This setting enables and disables the logging of neutral instantaneous overcurrent events in the
sequence of events recorder.
Figure 5-127: Neutral IOC1 logic
5.7.5 Wattmetric ground fault
5.7.5.1 Wattmetric zero-sequence directional (ANSI 32N, IEC PSDE)
SETTINGS
GROUPED ELEMENTS
SETTING GROUP 1(6)
WATTMETRIC...
WATTMETRIC GROUND FAULT 1(4)
WATTMETRIC
GROUND FAULT 1
WATTMETRIC GND FLT 1
FUNCTION: Disabled
Range: Disabled, Enabled
WATTMETRIC GND FLT 1
SOURCE: SRC 1
Range: SRC 1, SRC 2, SRC 3, SRC 4, SRC 5, SRC 6
WATTMETRIC GND FLT 1
VOLT: Calculated VN
Range: Calculated VN, Measured VX
WATTMETRIC GND FLT 1
OV PKP: 0.20 pu
Range: 0.02 to 3.00 pu in steps of 0.01
WATTMETRIC GND FLT 1
CURR: Calculated IN
Range: Calculated IN, Measured IG