CHAPTER 5: SETTINGS
CONTROL ELEMENTS
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
5-257
5
The easiest way to assign element outputs to a trip bus is through the EnerVista software under
Settings > Protection
Summary
. Navigate to a specific protection or control protection element and check the bus box by hovering over the
blank check box and selecting an option that displays. Once the required element is selected for a specific bus, a list of
element operate-type operands are displayed and can be assigned to a trip bus. If more than one operate-type operand is
required, it can be assigned directly from the trip bus menu.
Figure 5-140: Trip bus fields in the protection summary
The following settings are available.
TRIP BUS 1 BLOCK
— The trip bus output is blocked when the operand assigned to this setting is asserted.
TRIP BUS 1 PICKUP DELAY
— This setting specifies a time delay to produce an output depending on how output is used.
TRIP BUS 1 RESET DELAY
— This setting specifies a time delay to reset an output command. Set the time delay long enough
to allow the breaker or contactor to perform a required action.
TRIP BUS 1 INPUT 1
to
TRIP BUS 1 INPUT 16
— These settings select a FlexLogic operand to be assigned as an input to the trip
bus.
TRIP BUS 1 LATCHING
— This setting enables or disables latching of the trip bus output. This is typically used when lockout is
required or user acknowledgement of the relay response is required.
TRIP BUS 1 RESET
— The trip bus output is reset when the operand assigned to this setting is asserted. Note that the
RESET OP
operand is pre-wired to the reset gate of the latch, As such, a reset command from the front panel interface or via
communications resets the trip bus output.