6.WEIGHING MODE SETTING AND OPERATION
61
(
1
)
ON edge (0
→
1) of Tare subtraction bit (0th bit of n CH) triggers tare
subtraction, zero-clearing Net weight.
(
2
)
Feeding starts with all valves full open. When the weight reaches (Final-
SP1), SP1 signal turns ON (9th bit of n+3 CH) and the Comparison inhibit
time starts (if enabled). Travel of the raw material tank valve changes from
“large” to “medium”.
(
3
)
When the weight reaches (Final – SP2), SP2 signal turns ON (10th bit of n+3
CH) and the Comparison inhibit time starts (if enabled). Travel of the raw
material tank valve changes from “medium” to “small”.
(
4
)
When the weight reaches (Final – FF CPS.), SP3 signal turns ON (11th bit of
n+3 CH) and the Compare time starts (if enabled). Feed valve is totally
closed.
(
5
)
When the Compare time expires, Over/Under judgment is made. If the
weight exceeds the range of Over/Under set values, Over or Under signal is
raised.
(
6
)
Open the metering tank valve to discharge the material into the container.
Completion of discharge can be confirmed by checking Near zero signal (8th
bit of n+3 CH). Repeat steps (1) to (5) for the next container.
Use CJ1 or appropriate relay sequencers to open/close the Feed/
Discharge valves, and these sequencers are controlled by F159.