4.20.2 Bypass-inverter switchover function (Pr. 135 to Pr. 139, Pr. 159)
When the motor is operated at 60Hz (or 50Hz), more efficient operation can be performed by the commercial power
supply than by the inverter. When the motor cannot be stopped for a long time for the maintenance/inspection of the
inverter, it is recommended to provide the commercial power supply circuit.
To avoid commercial power supply being applied to the inverter output side when switching between inverter
operation and commercial power supply operation, provide an interlock which the MC of the commercial power
supply side turns on only when the MC of the inverter output side is off. Using the electronic bypass sequence
function that outputs the timing signal for operation of the magnetic contactor, a complicated commercial power
supply switchover interlock can be provided by the inverter.
The complicated sequence circuit for bypass operation is built in the inverter. Hence, merely inputting the start,
stop or automatic switchover selection signal facilitates the interlock operation of the switchover magnetic
contactor.
Parameter
Number
Name
Initial
Value
Setting
Range
Description
135
Electronic bypass sequence
selection
0
0
Without electronic bypass sequence
1
With electronic bypass sequence
136
MC switchover interlock time
1s
0 to 100s Set the operation interlock time of MC2 and MC3.
137
Start waiting time
0.5s
0 to 100s
Set the time slightly longer (0.3 to 0.5s or so) than the
time from when the ON signal enters MC3 until it
actually turns on.
138
Bypass selection at a fault
0
0
Inverter output is stopped (motor coast) at inverter
fault.
1
Operation is automatically switched to bypass
operation at inverter fault (Not switched when an
external thermal relay operation (E.OHT) or CPU
fault (E.CPU) occurs).
139
Automatic switchover frequency
from inverter to bypass operation
9999
0 to 60Hz
Set the frequency to switch inverter operation to
bypass operation.
Inverter operation is performed from a start until
Pr.
139
is reached, and when the output frequency is at
or above
Pr. 139
, inverter operation is automatically
switched to bypass operation.
9999
Without automatic switchover
159
Automatic switchover frequency
range from bypass to inverter
operation
9999
0 to 10Hz
Valid during automatic switchover operation (
Pr. 139
z
9999)
When the frequency command decreases below (
Pr.
139
-
Pr. 159
) after operation is switched from inverter
operation to bypass operation, the inverter
automatically switches operation to inverter operation
and operates at the frequency of frequency
command. When the inverter start command (STF/
STR) is turned off, operation is switched to inverter
operation also.
9999
Valid during automatic switchover operation (
Pr. 139
z
9999)
When the inverter start command (STF/STR) is
turned off after operation is switched from inverter
operation to bypass operation, operation is switched
to inverter operation and the motor decelerates to
stop.
The above parameters can be set when
Pr. 160 User group read selection
= "0".
(Refer to page 173.)