183
Selection of operation mode and
operation location
4
PA
R
A
M
E
T
E
R
S
4.18.2 Operation mode at power on (Pr. 79, Pr. 340)
(1) Specify operation mode at power on
(Pr. 340)
Depending on the
Pr. 79
and
Pr. 340
settings, the operation mode at power on (reset) changes as described below.
When power is switched on or when power comes back on after instantaneous power failure, the inverter can be
started up in network operation mode.
After the inverter has started up in the network operation mode, parameter write and operation can be performed
from a program.
Set this mode for communication operation using the RS-485 terminals or communication option.
Parameter
Number
Name
Initial
Value
Setting
Range
Description
79
Operation mode selection
0
0 to 4, 6, 7 Select the operation mode.
(Refer to page 177.)
340 *
Communication startup
mode selection
0
0
As set in
Pr. 79
.
1, 2
Started in network operation mode.
When the setting is "2", it will resume the pre-instantaneous
power failure operation mode after an instantaneous power
failure occurs.
10, 12
Started in network operation mode. Operation mode can be
changed between the PU operation mode and network
operation mode from the operation panel. When the setting is
"12", it will resume the pre-instantaneous power failure
operation mode after an instantaneous power failure occurs.
The above parameters can be changed during a stop in any operation mode.
* The parameters can be set when
Pr. 160 User group read selection
= "0". However, the parameters can be set whenever the communication option is
connected.
(Refer to page 173.)
.
Pr. 340
Setting
Pr. 79
Setting
Operation Mode at Power on, Power
Restoration, Reset
Operation Mode Switching
0
(initial
value)
0
(initial
value)
External operation mode
Switching among the External, PU, and NET operation mode
is enabled
*2
1
PU operation mode
Fixed to PU operation mode
2
External operation mode
Switching between the External and Net operation mode is
enabled
Switching to PU operation mode is disabled
3, 4
External/PU combined operation mode
Operation mode switching is disabled
6
External operation mode
Switching among the External, PU, and NET operation mode
is enabled while running
7
External operation mode when X12 (MRS) signal ON
Switching among the External, PU, and NET operation mode
is enabled
*2
External operation mode when X12 (MRS) signal OFF
Fixed to External operation mode (Forcibly switched to
External operation mode.)
1, 2
*1
0
NET operation mode
Same as when
Pr. 340
= "0"
1
PU operation mode
2
NET operation mode
3, 4
External/PU combined operation mode
6
NET operation mode
7
NET operation mode when X12 (MRS) signal ON
External operation mode when X12 (MRS) signal OFF
10, 12
*1
0
NET operation mode
Switching between the PU and NET operation mode is
enabled
*3
1
PU operation mode
Same as when
Pr. 340
= "0"
2
NET operation mode
Fixed to NET operation mode
3, 4
External/PU combined operation mode
Same as when
Pr. 340
= "0"
6
NET operation mode
Switching between the PU and NET operation mode is
enabled while running
*3
7
External operation mode
Same as when
Pr. 340
= "0"
*1
The
Pr. 340
setting "2" or "12" is mainly used for communication operation using the inverter RS-485 terminals. When a value other than "9999" (selection
of automatic restart after instantaneous power failure) is set in
Pr. 57 Restart coasting time
, the inverter will resume the same operation state which was in
before after power has been restored from an instantaneous power failure.
When
Pr. 340
= "1, 10", a start command turns off if power failure has occurred and then restored during a start command is on.
*2
The operation mode cannot be switched directly between the PU operation mode and network operation mode.
*3
Operation mode can be changed between the PU operation mode and network operation mode with
key of the operation panel (FR-DU07) and X65 signal.
i
Parameters referred to
i
Pr. 57 Restart coasting time
Refer to page 136.
Pr. 79 Operation mode selection
Refer to page 175.
Содержание F700
Страница 327: ...318 MEMO ...
Страница 340: ...331 MEMO ...