116
Function assignment of external
terminal and control
4.10.5 Output terminal function selection (Pr. 190 to Pr. 196)
(1) Output signal list
You can set the functions of the output terminals.
Refer to the following table and set the parameters: (0 to 99: Positive logic, 100 to 199: Negative logic)
You can change the functions of the open collector output terminal and relay output terminal.
Parameter
Number
Name
Initial
Value
Initial Signal
Setting Range
190
RUN terminal
function selection
Open
collector
output
terminal
0
RUN (inverter running)
0 to 5, 7, 8, 10 to 19, 25, 26,
45 to 48, 64, 70 to 79, 85, 90 to 96,
98, 99, 100 to 105, 107, 108, 110 to
116, 125, 126, 145 to 148, 164,
170, 179, 185, 190 to 196, 198,
199, 9999
191
SU terminal function
selection
1
SU (up to frequency)
192
IPF terminal function
selection
2
IPF (instantaneous power
failure, undervoltage)
193
OL terminal function
selection
3
OL (overload alarm)
194
FU terminal function
selection
4
FU (output frequency
detection)
195
ABC1 terminal
function selection
Relay
output
terminal
99
ALM (fault output)
0 to 5, 7, 8, 10 to 19, 25, 26, 45 to
48, 64, 70 to 79, 85, 90, 91, 94 to
96, 98, 99, 100 to 105, 107, 108,
110 to 116, 125, 126, 145 to 148,
164, 170, 179, 185, 190, 191, 194
to 196, 198, 199, 9999
196
ABC2 terminal
function selection
9999
No function
The above parameters can be set when
Pr. 160 User group read selection
= "0".
(Refer to page 173)
Setting
Signal
Name
Function
Operation
Related
Parameters
Refer
to Page
Positive
Logic
Negative
Logic
0
100
RUN
Inverter running
Output during operation when the inverter
output frequency rises to or above
Pr. 13
Starting frequency
.
118
1
101
SU
Up to frequency
*1
Output when the output frequency is
reached to the set frequency.
Pr. 41
120
2
102
IPF
Instantaneous power
failure/undervoltage
Output at occurrence of an instantaneous
power failure or when undervoltage
protection is activated.
Pr. 57
136
3
103
OL
Overload alarm
Output while stall prevention function is
activated.
Pr. 22, Pr. 23,
Pr. 66, Pr. 148,
Pr. 149, Pr. 154
70
4
104
FU
Output frequency
detection
Output when the output frequency reaches
the frequency setting in
Pr. 42
(
Pr. 43
for
reverse rotation).
Pr. 42, Pr. 43
120
5
105
FU2
Second output
frequency detection
Output when the output frequency reaches
the frequency setting in
Pr. 50
.
Pr. 50
120
7
107
RBP
Regenerative brake
pre-alarm
Output when 85% of the regenerative brake
duty set in
Pr. 70
is reached.
Setting can be made for the 01800 or more.
Pr. 70
102
8
108
THP
Electronic thermal O/
L relay pre-alarm
Output when the electronic thermal value
reaches 85% of the trip level.
(Electronic thermal relay function protection
(E.THT/E.THM) actirates, when the value
reached 100%.)
Pr. 9
97
10
110
PU
PU operation mode
Output when the PU operation mode is
selected.
Pr. 79
175
11
111
RY
Inverter operation
ready
Output when the reset process is completed
(when the inverter can be started by
switching the start signal on or while it is
running) after powering on the inverter.
118
12
112
Y12
Output current
detection
Output when the output current is higher
than the
Pr. 150
setting for longer than the
time set in
Pr. 151
.
Pr. 150, Pr. 151
121
13
113
Y13
Zero current
detection
Output when the output power is lower than
the
Pr. 152
setting for longer than the time
set in
Pr. 153
.
Pr. 152, Pr. 153
121