156
Frequency setting by analog input (terminal 1, 2, 4)
(1) Selection of analog input selection
For the terminals 2, 4 used for analog input, voltage input (0 to 5V, 0 to 10V) or current input (4 to 20mA) can be
selected.
Change parameters (
Pr.73, Pr.267
) and a voltage/current input switch (switch 1, 2) to change input specifications.
Rated specifications of terminal 2 and 4 change according to the voltage/current input switch setting.
Voltage input:
Input resistance 10k
:
± 1k
:
, Maximum permissible voltage 20VDC
Current input: Input resistance 245
:
± 5
:
, Maximum permissible current 30mA
Switch 1:Terminal 4 input
ON: Current input (initial status)
OFF: Voltage input
Switch 2: Terminal 2 input
ON: Current input
OFF: Voltage input (initial status)
CAUTION
Set
Pr.73, Pr.267
, and a voltage/current input switch correctly, then input an analog signal in accordance with the
setting. Incorrect setting as in the table below could cause component damage. Incorrect settings other than
below can cause abnormal operation.
Voltage/current
input switch
2
4
Switch 1
Switch 2
Setting Causing Component Damage
Operation
Switch setting
Terminal input
ON
(Current input)
Voltage input
This could cause component damage to the analog signal output circuit of signal
output devices. (electrical load in the analog signal output circuit of signal output
devices increases)
OFF
(Voltage input)
Current input
This could cause component damage of the inverter signal input circuit. (output
power in the analog signal output circuit of signal output devices increases)