131
Monitor display and monitor output signal
4
PA
R
A
M
E
T
E
R
S
4.11.3 CA, AM terminal function selection (Pr.55, Pr.56, Pr.867, Pr.869)
(1) Frequency monitoring reference(
Pr. 55
)
(2) Current monitoring reference (
Pr. 56
)
For signal output, two different output terminals are available: analog current output terminal CA and analog
output terminal AM.
You can select the signals output to the terminals CA, AM.
Parameter
Number
Name
Initial Value
Setting Range
Description
55 *
Frequency monitoring
reference
50Hz
0 to 400Hz
Full-scale value when frequency
monitor value is output to terminal CA
and AM.
56 *
Current monitoring
reference
Rated inverter
current
01160 or
less
0 to 500A
Full-scale value when current monitor
value is output to terminal CA and AM.
01800 or
more
0 to
3600A
867
AM output filter
0.01s
0 to 5s
Set the output filter of terminal AM.
869
Current output filter
0.02s
0 to 5s
Adjust response level of current output.
The above parameters can be set when
Pr. 160 User group read selection
= "0".
(Refer to page 173)
* The above parameters allow its setting to be changed during operation in any operation mode even if "0" (initial value) is set
in
Pr. 77 Parameter write selection
.
• Set the full scale value when outputting the frequency monitor from
terminal CA or AM.
• For the calibration of terminal CA, set the full-scale value of the
connected meter when output current of terminal CA is 20mADC.
Set the frequency to be indicated as the full scale value on the meter
(20mADC ammeter) connected between terminal CA and 5. (For
example, 60Hz or 120Hz)
Output voltage is proportional to the frequency. (Maximum output
current is 20mADC.)
• For the calibration of terminal AM, set the full-scale value of the
connected meter when output voltage of terminal AM is 10VDC.
Set the frequency to be indicated as the full scale value on the meter
(10VDC voltmeter) connected between terminal AM and 5. (For
example, 60Hz or 120Hz)
Output voltage is proportional to the frequency. (Maximum output
voltage is 10VDC.)
• Set the full scale value when outputting the current monitor from
terminal CA or AM.
• For the calibration of terminal CA, set the full-scale value of the
connected current meter when the output current of terminal CA is
20mADC.
Set the current to be indicated as the full scale value on the meter
(20mADC ammeter) connected between terminal CA and 5.
Output current is proportional to the monitored value of output
current. (Maximum output current is 20mADC.)
• For the calibration of terminal AM, set the full-scale value of the
connected current meter when the output voltage of terminal AM is
10VDC.
Set the current to be indicated as the full scale value on the meter
(10VDC voltmeter) connected between terminal AM and 5.
Output voltage is proportional to the monitored value of output
current. (Maximum output voltage is 10VDC.)
Setting range of
Pr. 55
1Hz
400Hz
50Hz
(initial value)
T
erminal CA
output current
T
erminal
AM
output voltage
(20mADC)
(10VDC)
Setting range of
Pr. 56
Rated output current
(initial value)
500A
(3600A)
T
erminal CA
output current
T
erminal
AM
output voltage
(20mADC)
(10VDC)
Содержание F700