127
Monitor display and monitor output signal
4
PA
R
A
M
E
T
E
R
S
Converter output
voltage
0.1V
8
*1
8
400V class:
800V
Displays the DC bus voltage value
Regenerative
brake duty
0.1%
9
*1
9
Pr. 70
Brake duty set in
Pr. 30
and
Pr. 70
(Setting
can be made for the 01800 or more)
Electronic thermal
relay function load
factor
0.1%
10
*1
10
100%
Displays the motor thermal cumulative
value on the assumption that the thermal
operation level is 100%.
Output current
peak value
0.01A/0.1A
*5
11
*1
11
Pr. 56
Retains the peak value of the output
current monitor and displays (clears at
every start)
Converter output
voltage peak value
0.1V
12
*1
12
400V class:
800V
Retains the peak value of the DC bus
voltage value and displays (clears at every
start)
Input power
0.01kW/
0.1kW
*5
13
*1
13
Rated inverter
power
u
2
Displays power of the inverter input side
Output power
0.01kW/
0.1kW
*5
14
*1
14
Rated inverter
power
u
2
Displays power of the inverter output side
Load meter
0.1%
17
17
100%
Displays the torque current in % on the
assumption that the
Pr. 56
setting is 100%
Cumulative
energization time
*2
1h
20
u
Displays the cumulative energization time
since the inverter shipment
You can check the numbers of the monitor
value exceeded 65535h with
Pr. 563
.
Reference voltage
output
21
Terminal CA: 20mA is output
Terminal AM: 10V is output
Actual operation
time
ޓ
*2*3
1h
23
u
Displays the cumulative inverter running
time.
You can check the numbers of the monitor
value exceeded 65535h with
Pr. 564
.
Use
Pr. 171
to clear the value.
(Refer to page 130 .)
Motor load factor
0.1%
24
24
200%
Displays the output current value in % on
the assumption that the rated inverter
current value is 100%.
Monitor value = output current monitor
value/rated inverter current
u
100 [%]
Cumulative power
*6
0.01kWh/
0.1kWh
*4, *5
25
u
Displays the cumulative power amount
according to the output power monitor
Use
Pr. 170
to clear the value.
(Refer to page 130.)
Power saving
effect
Variable
according
to
parameters
50
50
Inverter
capacity
Displays energy saving effect monitor
You can change the monitor to power
saving, power saving average value,
charge display and % display using
parameters.
(For details, refer to page 149.)
Cumulative saving
power
*6
51
u
PID set point
0.1%
52
52
100%/
C42 or C44
Displays the set point, measured value and
deviation during PID control
(For details, refer to page 226.)
PID measured
value
0.1%
53
53
100%/
C42 or C44
PID deviation
0.1%
54
u
Input terminal
status
55
*1
u
Displays ON/OFF status of the input
terminal on the PU
(Refer to page 129 for DU display)
Output terminal
status
*1
u
Displays ON/OFF status of the output
terminal on the PU
(Refer to page 129 for DU display)
Option input
terminal status
56
u
u
Displays ON/OFF status of the input
terminal of the digital input option (FR-
A7AX) on the DU
(refer to page 129 for
details)
Option output
terminal status
57
u
u
Displays ON/OFF status of the output
terminal of the digital output option (FR-
A7AY) and relay output option (FR-A7AR)
on the DU
(refer to page 129 for details)
Types of Monitor
Increments
Pr. 52
Parameter
Setting Value
Pr. 54
(CA)
Pr. 158
(AM)
Parameter
Setting
Value
Full-scale
value of the
terminal CA
and AM
Description
DU LED
PU main
monitor