166
Frequency setting by analog input (terminal 1, 2, 4)
(c) Method to adjust only the frequency without adjustment of a gain voltage (current).
(When changing the gain frequency from 50Hz to 60Hz)
REMARKS
Changing
C4 (Pr. 903)
or
C7 (Pr. 905)
(gain adjustment) value will not change the
Pr. 20
value. The input of terminal 1 (frequency
setting auxiliary input) is added to the speed setting signal.
For the operating procedure using the parameter unit (FR-PU04/FR-PU07), refer to the FR-PU04/FR-PU07 instruction manual.
When setting the value to 120Hz or more, it is necessary to set
Pr. 18 High speed maximum frequency
to 120Hz or more.
(Refer to
page 76)
Make the bias frequency setting using
calibration parameter C2 (Pr. 902) or C5 (Pr. 904).
(Refer to page 163)
CAUTION
Be cautious when setting any value other than "0" as the bias frequency at 0V (0mA). Even if a speed command
is not given, merely turning on the start signal will start the motor at the preset frequency.
i
Parameters referred to
i
Pr. 20 Acceleration/deceleration reference frequency
Refer to page 90
Pr. 73 Analog input selection, Pr. 267 Terminal 4 input selection
Refer to page 155
Pr. 79 Operation mode selection
Refer to page 175
Display
Operation
Flicker...Parameter setting complete!!
1.
Pr. 125
) or
(
Pr. 126
) appears.
4.
Press to set.
5.
Mode/monitor check
Press twice to choose the
monitor/frequency monitor.
or
Terminal 2 input
Terminal 4 input
Terminal 2 input Terminal 4 input
3.
Turn
to change the set value to
" ". (60.00Hz)
2.
Press to show the present set value.
(50.00Hz)
6.
Apply a voltage across the inverter
terminals 2-5 (across 4-5) and turn on the
start command (STF, STR).
Operation starts at 60Hz.