144
Operation setting at fault occurrence
Use
Pr. 65
to select the fault to be activated for retries. No retry will be made for the fault not indicated. (Refer to
page
270
for the fault description.)
z
indicates the errors selected for retry.
Fault for
Retry
Pr. 65
Setting
Fault for
Retry
Pr. 65
Setting
0
1
2
3
4
5
0
1
2
3
4
5
E.OC1
z
z
z
z
z
E. GF
z
z
E.OC2
z
z
z
z
E.OHT
z
E.OC3
z
z
z
z
z
E.OLT
z
z
E.OV1
z
z
z
z
E.OPT
z
z
E.OV2
z
z
z
z
E.OP1
z
z
E.OV3
z
z
z
z
E. PE
z
z
E.THM
z
E.PTC
z
E.THT
z
E.CDO
z
z
E.IPF
z
z
E.SER
z
z
E.UVT
z
z
E.ILF
z
z
E.BE
z
z
E.PID
z
z
CAUTION
For a retry error, only the description of the first fault is stored.
When an inverter fault is reset by the retry function at the retry time, the accumulated data of the electronic thermal relay
function, regenerative brake duty etc. are not cleared. (Different from the power-on reset.)
Retry is not performed if E.PE (Parameter storage device fault) occurred at power on.
CAUTION
When you have selected the retry function, stay away from the motor and machine in the case of the inverter is
tripped. The motor and machine will start suddenly (after the reset time has elapsed) after the inverter trip.
When you have selected the retry function, apply in easily visible places the CAUTION stickers supplied.
i
Parameters referred to
i
Pr. 57 Restart coasting time
Refer to page 136
Содержание F700
Страница 327: ...318 MEMO ...
Страница 340: ...331 MEMO ...