5-18
F650 DIGITAL BAY CONTROLLER
GEK-106310-AF
5.2 PRODUCT SETUP
CHAPTER 5: SETPOINTS
Reverse: The polarity of the current transformers is
inverted. Voltage and current are 180º out of phase.
States associated with the fault report (
Actual >Status>Records Status > Fault Reports
), are shown on Table 5-7: Fault
Table 5-7: Fault report states
FAULT REPORT TRIGG:
The activation of this state initiates the calculation of the fault location and the generation
of the corresponding report.
CLEAR FAULT REPORTS:
The activation of this state produces the removal of all faults stored in the relay.
Additionally, all active faults on the HMI display are acknowledged. This signal is
programmed at “
Setpoint>Relay Configuration>Protection Elements
”.
FAULT DATE:
Date and time of the last fault.
FAULT TYPE:
Type of the last fault produced (3PHASE, AG, BG, CG, AB, ABG, BC, BCG, CA, CAG, NAF). NAF
indicates that the type of fault has not been calculated.
FAULT LOCATION:
Calculated distance to the last fault (the metering element is the same used for setting the
line length).
FAULT REPORT NUMBER:
Number of the fault report file saved in the relay’s non-volatile memory, associated with
the last fault produced.
5.2.3.2 Fault report retrieval
Fault report files can be retrieved using the EnerVista 650 Setup software, or the web server at "http:\\relay IP address".
To obtain fault reports using the EnerVista 650 Setup software, go to
Actual > Records > Fault report
. The top of the
window shows the number of the last fault report stored by the device (Fault Record Number). Click
View header
to see the
header of the record selected under
Select Record
.
Click
Download
to retrieve the file and save in a selected folder. The file name is “FLTxxx.TXT”, where xxx is the
corresponding record number. Fault report retrieval uses either serial communication (ModBus RTU) or Ethernet (ftp, tftp).
Fault reports are stored in the relay’s non-volatile memory, so they are accessible from the EnerVista 650 Setup software
or the relay’s web server. The fault report is a text file named FLTxxx.txt where xxx is the record number, with a range of
001 to 999. Only files from the 10 last faults are stored. If there are already ten files stored and a new fault occurs, the new
fault overwrites the oldest one. If
Show Fault on HMI
is enabled, real-time fault information is also displayed on the HMI.
When a fault is produced and a warning message is displayed on the HMI, fault information alternates between two
separate screens: one with general information, and a second with the fault metering values. This screen needs to be
acknowledged by the user to exit the fault report screen. If several consecutive faults are produced, the HMI displays the
most recent one. Each stored fault needs to be acknowledged (up to a maximum of 10 faults). The HMI menu offers an
option to view the last 10 faults produced, with both the general information screen and the metering screen available for
each fault.
FAULT REPORT STATES
FAULT REPORT TRIGG
CLEAR FAULT REPORTS
FAULT DATE
FAULT TYPE
FAULT LOCATION
FAULT REPORT NUMBER
Содержание F650
Страница 68: ...2 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 2 6 EXTERNAL CONNECTIONS CHAPTER 2 PRODUCT DESCRIPTION ...
Страница 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Страница 660: ...7 254 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 7 3 IEC 61850 CONFIGURATOR CHAPTER 7 IEC 61850 PROTOCOL ...
Страница 734: ...12 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 12 4 RELAY CONFIGURATION CHAPTER 12 FREQUENTLY ASKED QUESTIONS ...
Страница 772: ...A 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF A 1 OPERANDS F650 MODEL FX GX APPENDIX A LOGIC OPERANDS ...
Страница 950: ...c 24 F650 DIGITAL BAY CONTROLLER GEK 106310 AF C 8 ANALOG INPUTS APPENDIX C DNP 3 0 PROTOCOL FOR F650 ...
Страница 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Страница 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Страница 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Страница 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1044: ...I 40 F650 DIGITAL BAY CONTROLLER GEK 106310 AF I 2 FACTORY DEFAULT CONFIGURATION APPENDIX I FACTORY DEFAULT CONFIGURATION ...
Страница 1046: ...J 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF J 1 GE MULTILIN WARRANTY APPENDIX J MISCELLANEOUS ...