CHAPTER 10: COMMISSIONING
10.3 GENERAL CONSIDERATIONS, POWER SUPPLY NETWORK
GEK-106310-AF
F650 DIGITAL BAY CONTROLLER
10-3
10.3 General considerations, power supply network
All devices running on AC current are affected by frequency. As a non-sine wave is the result of a fundamental wave plus a
series of harmonics from this fundamental wave, we can infer that devices running on AC current are influenced by the
applied waveform.
For a correct testing of relays running on AC current, it is fundamental to use a current and/or voltage senoidal waveform.
The pureness of a senoidal wave (lack of harmonics) cannot be expressed specifically for a specific relay. However, any
relay incorporating sintonized circuits, R-L and R-C circuits, is affected by non-senoidal waveforms, as in the case of F650.
These relays respond to the voltage waveform in a different way to the majority of AC current voltmeters. If the power
supply network used for the testing contains wide harmonics, the voltmeter and relay responses are different.
Relays have been calibrated in factory using a Network of 50 or 60 Hz with a minimum harmonic content. When the relay
is tested, a power supply network with no harmonics in its waveform must be used.
The ammeters and chronometers used for testing the pickup current and relay operation time must be calibrated and
their accuracy must be better than the relay’s. The power supply used in the tests must remain stable, mainly in the levels
near the operation thresholds.
It is important to point out that the accuracy with which the test is performed depends on the network and on the
instruments used. Functional tests performed with unsuitable power supply network and instruments are useful to check
that the relay operates properly and therefore its operating characteristics are verified in an approximate manner.
However, if the relay would be calibrated in these conditions, its operational characteristics would be outside the tolerance
range values.
The following sections detail the list of tests for verifying the complete relay functionality.
Содержание F650
Страница 68: ...2 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 2 6 EXTERNAL CONNECTIONS CHAPTER 2 PRODUCT DESCRIPTION ...
Страница 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Страница 660: ...7 254 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 7 3 IEC 61850 CONFIGURATOR CHAPTER 7 IEC 61850 PROTOCOL ...
Страница 734: ...12 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 12 4 RELAY CONFIGURATION CHAPTER 12 FREQUENTLY ASKED QUESTIONS ...
Страница 772: ...A 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF A 1 OPERANDS F650 MODEL FX GX APPENDIX A LOGIC OPERANDS ...
Страница 950: ...c 24 F650 DIGITAL BAY CONTROLLER GEK 106310 AF C 8 ANALOG INPUTS APPENDIX C DNP 3 0 PROTOCOL FOR F650 ...
Страница 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Страница 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Страница 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Страница 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1044: ...I 40 F650 DIGITAL BAY CONTROLLER GEK 106310 AF I 2 FACTORY DEFAULT CONFIGURATION APPENDIX I FACTORY DEFAULT CONFIGURATION ...
Страница 1046: ...J 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF J 1 GE MULTILIN WARRANTY APPENDIX J MISCELLANEOUS ...