4-14
F650 DIGITAL BAY CONTROLLER
GEK-106310-AF
4.1 ENERVISTA 650 SETUP SOFTWARE
CHAPTER 4: INTERFACES, SETTINGS & ACTUAL VALUES
For example, if the Phase TOC High element is configured in the source *.650 file as described below:
1. Note that fields in blue contain default values
CASE 1:
If the setting groups option is disabled (
Setpoint > Control Elements > Setting group
) in the source file, conversion
is performed in the destination file as follows:
•
Settings of different elements (Phase TOC High 1, 2 and 3) that belong to Setting group 1(SG1) in the source file are
copied into elements that belong to Setting Group 1 in the destination file.
•
Elements in the other setting groups are configured with default values in the configuration file.
CASE 2:
If the setting groups option is enabled (
Setpoint > Control Elements > Setting group
) in the source file, conversion
to the destination file is as follows:
•
Settings of different elements (Phase TOC High 1, 2 and 3) that belong to different setting groups in the source file are
copied into elements that belong to first group of first three setting groups in the destination file
•
Protection elements in the other groups/setting groups are configured with default values in the destination file.
Phase TOC High
Phase TOC High 1 (G1)
Phase TOC High 2
(G2)
Phase TOC High 3(G3)
Function
ENABLED
ENABLED
ENABLED
Input
PHASOR(DFT)
PHASOR(DFT)
PHASOR(DFT)
Pickup Level
0.10
1.50
2.00
Curve
Definite time
Definite time
Definite time
TD Multiplier
0.02
0.05
0.1
Reset
INSTANTANEOUS
INSTANTANEOUS
INSTANTANEOUS
Voltage Restraint
DISABLED
DISABLED
DISABLED
Snapshot Events
ENABLED
ENABLED
ENABLED
SG1
SG2
SG3
SG4
SG5
SG6
Phase TOC High
G1
G2
G3
G1
G2
G3
G1
G2
G3
G1
G2
G3
G1
G2
G3
G1
G2
G3
Function
ENABLED
DISABLED
Input
PHASOR(DFT)
Pickup Level
0.10
1.50
2.00
1.00
Curve
Definite time
IEEE Ext Inv
TD Multiplier
0.02
0.05
0.10
1.00
Reset
INSTANTANEOUS
Voltage
Restraint
DISABLED
Snapshot Events
ENABLED
SG1
SG2
SG3
SG4
SG5
SG6
Phase TOC High
G1
G2
G3
G1
G2
G3
G1
G2 G3 G1 G2 G3 G1 G2 G3 G1 G2 G3
Function
ENABLED DISABLED
ENABLED
DISABLED
ENABLED
DISABLED
Input
PHASOR(DFT)
Pickup Level
0.10
1.00
1.50
1,00
2.00
1.00
Curve
Definite
time
IEEE Ext
Inv
Definite time IEEE Ext Inv Definite time
IEEE Ext Inv
TD Multiplier
0.02
1.00
0.05
1,00
0.10
1.00
Reset
INSTANTANEOUS
Voltage
Restraint
DISABLED
Snapshot
Events
ENABLED
Содержание F650
Страница 68: ...2 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 2 6 EXTERNAL CONNECTIONS CHAPTER 2 PRODUCT DESCRIPTION ...
Страница 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Страница 660: ...7 254 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 7 3 IEC 61850 CONFIGURATOR CHAPTER 7 IEC 61850 PROTOCOL ...
Страница 734: ...12 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 12 4 RELAY CONFIGURATION CHAPTER 12 FREQUENTLY ASKED QUESTIONS ...
Страница 772: ...A 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF A 1 OPERANDS F650 MODEL FX GX APPENDIX A LOGIC OPERANDS ...
Страница 950: ...c 24 F650 DIGITAL BAY CONTROLLER GEK 106310 AF C 8 ANALOG INPUTS APPENDIX C DNP 3 0 PROTOCOL FOR F650 ...
Страница 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Страница 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Страница 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Страница 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1044: ...I 40 F650 DIGITAL BAY CONTROLLER GEK 106310 AF I 2 FACTORY DEFAULT CONFIGURATION APPENDIX I FACTORY DEFAULT CONFIGURATION ...
Страница 1046: ...J 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF J 1 GE MULTILIN WARRANTY APPENDIX J MISCELLANEOUS ...