APPENDIX B: MODBUS PROTOCOL
B.2 MODBUS F650
GEK-106310-AF
F650 DIGITAL BAY CONTROLLER
B-3
The following table shows the generic string format, valid for transmission and reception. However, each function has its
own particularities, as described later in this manual.
MODBUS FORMAT
CLIENT ADDRESS
[A]
1 byte
Each device in a communications bus must have a unique address to prevent two
units from responding at the same time to the same request. All relay ports use this
address, which can be programmed to any value between 1 and 254.
When the master transmits a string with the slave address 0, this indicates that it is a
Broadcast. Every slave in the communication bus performs the requested action, but
none of them responds to the master. Broadcast is only accepted for writing since no
unit responds.
FUNCTION CODE
[B]
1 byte
This is one of the function codes supported by the equipment. The generic function
codes are 3 and 4 for reading and 16 for writing. Special read function 66 and write
function 67 are available only for firmware version 7.50 or above.
When the slave responds with an exception to any of these strings, it places to 1 the
most important bit of the corresponding function. For example, an exception to
function 3 is indicated with an 83 as function code, and an exception to function 16
or 0x10 in hexadecimal, is indicated with a 0x90.
SETTING GROUP SELECTED
[B1]
1byte
This part of string format only applies to read function 66 and write function 67 (fw
7.50 or above).This byte indicates the setting group being read or written. Values
should are as follow:
0 [Decimal]
Setting Group 1
1 [Decimal]
Setting Group 2
…
5 [Decimal]
Setting Group 6
DATA
[C]
N bytes
This section includes a variable number of bytes, depending on the function code. It
may include: addresses, data length, settings, commands or exception codes sent by
the client.
CRC
[D]
2 bytes
Two-byte control code. ModBus/RTU includes a 16-bit CRC in each string for error
detection. If the slave detects a string with errors, based on an incorrect CRC, it
neither performs an action, nor responds to the master. The CRC order is LSB-MSB.
TIME OUT
Required time to
transmit 3.5 Bytes
A string is finished when nothing is received during a period of 3.5 bytes, with the
actual time varying depending on baud rate:
15 ms at 2400 bps
2 ms at 19200 bps
300
μ
s at 115200 bps
etc.
Содержание F650
Страница 68: ...2 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 2 6 EXTERNAL CONNECTIONS CHAPTER 2 PRODUCT DESCRIPTION ...
Страница 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Страница 660: ...7 254 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 7 3 IEC 61850 CONFIGURATOR CHAPTER 7 IEC 61850 PROTOCOL ...
Страница 734: ...12 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 12 4 RELAY CONFIGURATION CHAPTER 12 FREQUENTLY ASKED QUESTIONS ...
Страница 772: ...A 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF A 1 OPERANDS F650 MODEL FX GX APPENDIX A LOGIC OPERANDS ...
Страница 950: ...c 24 F650 DIGITAL BAY CONTROLLER GEK 106310 AF C 8 ANALOG INPUTS APPENDIX C DNP 3 0 PROTOCOL FOR F650 ...
Страница 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Страница 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Страница 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Страница 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1044: ...I 40 F650 DIGITAL BAY CONTROLLER GEK 106310 AF I 2 FACTORY DEFAULT CONFIGURATION APPENDIX I FACTORY DEFAULT CONFIGURATION ...
Страница 1046: ...J 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF J 1 GE MULTILIN WARRANTY APPENDIX J MISCELLANEOUS ...