CHAPTER 5: SETPOINTS
5.6 INPUTS/OUTPUTS
GEK-106310-AF
F650 DIGITAL BAY CONTROLLER
5-143
In order to implement these schemes, it is not necessary to set any setting in the element. Internal functions are always
operative and provide the following logic operands:
Table 5-87: Supervision logic operands
A continuity failure is detected in a circuit when both voltage detectors (Va and Vb) detect lack of voltage during more than
500 ms. This function is not influenced by the breaker status.
These operands can be associated with internal signals (virtual outputs), LEDs or element outputs, to issue alarm signals or
to block elements, for example for blocking the Breaker close if an anomaly is detected in the trip circuit.
Available schemes are as follows:
1.
Without supervision
2.
With current supervision (with seal-in)
3.
With simple voltage supervision
4.
With double voltage supervision
5.
With current and simple voltage supervision (with seal-in)
6.
With current and double voltage supervision (with seal-in)
7.
With current and double voltage supervision (with seal-in) and serial resistor in voltage monitors.
The following subsections describe the different types of connection to create each supervision scheme in an easy way. As
the supervision circuits are identical, only the first group connection examples are described, being also applicable to the
second group.
In order to assure a high isolation level between groups, the digital inputs for supervision have been located in a
symmetrical basis. That is to optimize the isolation between groups that can be connected to different batteries, and
therefore requiring a greater distance between circuits.
Actual > Inputs/Outputs > Contact inputs > Board X
Being X the corresponding board in each case
OPERAND
DESCRIPTION
CONT IP_X_CC9 (Va_COIL1)
Active when voltage is detected in terminals F1 - F2 (circuit 1)
CONT IP_X_CC10 (Vb_COIL1)
Active when voltage is detected in terminals F3 - F4 (circuit 1)
CONT IP_X_CC11 (Va_COIL2)
Active when voltage is detected in terminals F15 - F16 (circuit 2)
CONT IP_X_CC12 (Vb_COIL2)
Active when voltage is detected in terminals F17 - F18 (circuit 2)
CONT IP_X_CC13 (O7_SEAL)
Active if current is detected by sensor in output O7 (F31-F33)
CONT IP_X_CC14 (O8_SEAL)
Active if current is detected by sensor in output O8 (F34-F36)
CONT IP_X_CC15 (SUP_COIL1)
Active when continuity is detected in circuit 1
CONT IP_X_CC16 (SUP_COIL2)
Active when continuity is detected in circuit 2
Содержание F650
Страница 68: ...2 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 2 6 EXTERNAL CONNECTIONS CHAPTER 2 PRODUCT DESCRIPTION ...
Страница 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Страница 660: ...7 254 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 7 3 IEC 61850 CONFIGURATOR CHAPTER 7 IEC 61850 PROTOCOL ...
Страница 734: ...12 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 12 4 RELAY CONFIGURATION CHAPTER 12 FREQUENTLY ASKED QUESTIONS ...
Страница 772: ...A 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF A 1 OPERANDS F650 MODEL FX GX APPENDIX A LOGIC OPERANDS ...
Страница 950: ...c 24 F650 DIGITAL BAY CONTROLLER GEK 106310 AF C 8 ANALOG INPUTS APPENDIX C DNP 3 0 PROTOCOL FOR F650 ...
Страница 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Страница 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Страница 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Страница 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1044: ...I 40 F650 DIGITAL BAY CONTROLLER GEK 106310 AF I 2 FACTORY DEFAULT CONFIGURATION APPENDIX I FACTORY DEFAULT CONFIGURATION ...
Страница 1046: ...J 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF J 1 GE MULTILIN WARRANTY APPENDIX J MISCELLANEOUS ...