5-36
F650 DIGITAL BAY CONTROLLER
GEK-106310-AF
5.3 SYSTEM SETUP
CHAPTER 5: SETPOINTS
5.3.4 Breaker settings
There are two types of breaker settings:
Breaker settings:
These settings correspond to the switchgear configured as a breaker in the F650; this switchgear is used
in the recloser functions, breaker failure and synchronism.
Breaker Maintenance:
These settings correspond to the initialization of the (KI)
2
t counters, and the counting of the number
of openings and closings of the switchgear configured as a breaker.
Breaker settings are as follows:
Number of switchgear:
This is the Number of the Switchgear that is configured as a breaker. It is the reference for
breaker failure (50BF), recloser (79) and synchronism (25) elements. The selected
switchgear in the breaker settings must be previously configured at
Setpoint > Relay
Configuration > Switchgear
. The relay allows to configure up to 16 switchgear elements,
but the one configured as a breaker is the reference for (KI)
2
t, openings and closings
counters.
Maximum (KI)
2
t:
This is the maximum set value for the square of the current multiplied by the breaker
opening time. There is a separate counter for each phase, but the value stored as the
maximum is a single value for the three phases.
(KI)
2
t Integration Time:
This is the integration time taken as the base (fixed opening time) for the calculation of
(KI)
2
t.
Maximum Openings:
This is the maximum number of openings allowed in the relay, with a limit of 9999; once
this value is exceeded, the relay produces an alarm. When the limit 9999 is reached the
maximum openings counter starts from zero.
Maximum Openings in 1 hour:
This is the maximum number of openings allowed in the relay during one hour; once this
value is reached, the corresponding alarm signal is activated; this value is updated and
reset after one hour.
Snapshot Events:
This setting enables or disables the snapshot event generation for the breaker signals.
The interrupted current limit setting, fixes the Maximum breaker capacity (this value is set depending on the information
provided by the breaker manufacturer); the relay incorporates a (KI)
2
t counter for each phase, when a breaker opening
occurs, the counter increases its value (in primary values). If the flowing current is lower than the rated current, the relay
takes the rated current value for its calculations. When the accumulated counter for each phase reaches or exceeds the
set value, the corresponding alarm signal is activated.
The purpose of this function is to provide closer information of the current status of the breaker’s internal contacts. This is,
in order to ensure appropriate breaker maintenance, and to decrease the risk of damage when the breaker has suffered
severe operations during a long time. Once the breaker has been operated, and the preventive maintenance is in place,
the accumulated I
2
t values and the number of operations are reset to zero.
Setpoint > System Setup > Breaker > Breaker settings
Setting Description
Name
Default
Value
Step
Range
Number of Switchgear selected as breaker Number of Switchgear
1
1
[1 : 16]
Maximum value of (KI)
2
t
Maximum (KI)
2
t
9999.99
0.01(KA)
2
s
[0.00 : 9999.99]
(KI)
2
t integration time
(KI)
2
t Integ. Time
0.03
0.01s
[0.03 : 0.25]
Maximum number of openings
Maximum Openings
9999
1
[0 : 9999]
Maximum Openings in one hour
Max.Openings 1 hour
40
1
[1 : 60]
Snapshot Event generation
Snapshot Events
ENABLED
N/A
[DISABLED – ENABLED]
Содержание F650
Страница 68: ...2 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 2 6 EXTERNAL CONNECTIONS CHAPTER 2 PRODUCT DESCRIPTION ...
Страница 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Страница 660: ...7 254 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 7 3 IEC 61850 CONFIGURATOR CHAPTER 7 IEC 61850 PROTOCOL ...
Страница 734: ...12 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 12 4 RELAY CONFIGURATION CHAPTER 12 FREQUENTLY ASKED QUESTIONS ...
Страница 772: ...A 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF A 1 OPERANDS F650 MODEL FX GX APPENDIX A LOGIC OPERANDS ...
Страница 950: ...c 24 F650 DIGITAL BAY CONTROLLER GEK 106310 AF C 8 ANALOG INPUTS APPENDIX C DNP 3 0 PROTOCOL FOR F650 ...
Страница 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Страница 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Страница 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Страница 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1044: ...I 40 F650 DIGITAL BAY CONTROLLER GEK 106310 AF I 2 FACTORY DEFAULT CONFIGURATION APPENDIX I FACTORY DEFAULT CONFIGURATION ...
Страница 1046: ...J 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF J 1 GE MULTILIN WARRANTY APPENDIX J MISCELLANEOUS ...