CHAPTER 5: SETPOINTS
5.2 PRODUCT SETUP
GEK-106310-AF
F650 DIGITAL BAY CONTROLLER
5-11
"SNTP1 tab shall contain settings of main SNTP server.
"SNTP2 tab shall contain settings of back-up SNTP server.
If two SNTP servers are configured, F650 operation mode is described as follow:
NOTE:
SNTP settings take effect after rebooting the device.
5.2.1.7 Procome protocol settings
Communication settings for Procome protocol. For more detail information go to APPENDIX E in this manual.
When NONE is selected in the comm port setting the protocol is not enabled. The com1 selection enables Procome for the
com1 (remote) serial port.
Slave Number:is the Procome slave number.
Baud rate and parity for COM1 must be set in the
Setpoint>Communications>Serial Ports
menu.
5.2.1.8 IEC 870-5-103 protocol settings
Communication settings for IEC 60870-5-103 protocol. For more detailed information go to 5.13 Section in this manual.
DNP protocol is available for standard and IEC61850 models but it is not available IEC 60870-5-103 models.
If COMM Port is set to NONE, IEC 870-5-103 communication protocol is not available.
If the user sets a value different from 0 in the Synchronization Timeout setting, when this timer expires without receiving a
synchronization message, the Invalid bit is set in the time stamp of a time-tagged message.
Scenario
Expected behaviour
SNTP1 server= Available
SNTP2 server= Available
F650 shall be synchronized by SNTP1 server.
No alarm
SNTP1 server= Available
SNTP2 server= Not Available
F650 shall continue to be synchronized by SNTP1 server
No alarm
SNTP1 server= Not Available
SNTP2 server= Available
If SNTP1 server fails, F650 shall get synchronization from SNTP2
server. When SNTP1 server recovers, F650 shall switch to be
synchronized by SNTP1 server.
No alarm
SNTP1 server= Not Available
SNTP2 server= Not Available
"Not Syncronized" Alarm shall appear in local mimic
Product Setup > Communication settings >PROCOME
Name
Default Value
Step
Range
COMM Port
NONE
N/A
[NONE - COM1]
Slave Number
0
1
[0 : 254]
Product Setup > Communication settings >IEC 870-5-103
Name
Default Value
Step
Range
COMM Port
NONE
N/A
[NONE - COM1]
Slave Number
1
1
[0 : 254]
Synchronization Timeout
30 min
1
[0 : 1440]
Содержание F650
Страница 68: ...2 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 2 6 EXTERNAL CONNECTIONS CHAPTER 2 PRODUCT DESCRIPTION ...
Страница 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Страница 660: ...7 254 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 7 3 IEC 61850 CONFIGURATOR CHAPTER 7 IEC 61850 PROTOCOL ...
Страница 734: ...12 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 12 4 RELAY CONFIGURATION CHAPTER 12 FREQUENTLY ASKED QUESTIONS ...
Страница 772: ...A 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF A 1 OPERANDS F650 MODEL FX GX APPENDIX A LOGIC OPERANDS ...
Страница 950: ...c 24 F650 DIGITAL BAY CONTROLLER GEK 106310 AF C 8 ANALOG INPUTS APPENDIX C DNP 3 0 PROTOCOL FOR F650 ...
Страница 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Страница 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Страница 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Страница 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1044: ...I 40 F650 DIGITAL BAY CONTROLLER GEK 106310 AF I 2 FACTORY DEFAULT CONFIGURATION APPENDIX I FACTORY DEFAULT CONFIGURATION ...
Страница 1046: ...J 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF J 1 GE MULTILIN WARRANTY APPENDIX J MISCELLANEOUS ...