CHAPTER 5: SETPOINTS
5.5 CONTROL ELEMENTS
GEK-106310-AF
F650 DIGITAL BAY CONTROLLER
5-121
5.5.5 VT fuse failure element (VTFF)
Note
: The Switchgear element used in the
VT Fuse Failure
element is the one configured in the
Number of Switchgear
setting, inside
Breaker settings
at
Setpoint > Protection Element > Setting Group X > Breaker > Breaker Settings.
This
switchgear must have previously been configured at
Setpoint > Relay Configuration > Switchgear
The fuse failure detector is used to block protection elements that can operate incorrectly due to a partial or total voltage
loss. This loss can be caused by the voltage transformers secondary circuit protection fuse failure.
The fuse failure element has only two settings, one to enable or disable the element and the other to enable or disable the
snapshot event generation.
The fuse failure signal provided by the element (VT FUSE FAILURE) can be monitored at
Actual> Status > Control Elements
>VT Fuse Failure
5.5.5.1 Fuse failure algorithm
To detect different types of fuses failures, it is necessary to use different detection methods. In example, a fuse failure
indication with loss of one or two voltage phases provides a significant level of negative sequence voltage, instead of a loss
of all voltage phases which causes a very low positive sequence voltage, but any negative sequence voltage.
F650 elements detect fuse failure under three possible situations:
(1)Breaker closed and positive sequence voltage (V1) under an established value (V1<0.5 p.u.).
(2)Positive sequence voltage lower than 0.5 p.u (V1<0.5 p.u.) and positive sequence current higher than 0.075 p.u. (I1>0.075
p.u.).
(3)Ratio between the negative and positive voltage components (V2/V1) higher than 0.25.
With the activation of any of the three previous signals during a period longer than 80 ms, the fuse failure signal (VT FUSE
FAILURE) is activated. Once this signal is activated, it is latched until whatever caused it disappears; for this purpose the
following condition must be met:
(4)Positive sequence voltage higher than 0.75 p.u and positive sequence current lower than 0.05 p.u.
The fuse failure signal can be used to issue an alarm and/or to block elements that may operate incorrectly due to a
partial or total loss of voltage. Protection elements that are usually blocked by the fuse failure signal are voltage restraint
overcurrent elements, and directional elements. To configure the block of these elements it is necessary to enter the
Setpoint > Relay Configuration > Protection Elements
” menu and select as block input for protection elements, the fuse
failure operation signal.
Setpoint > Control Elements > VT Fuse Failure
setting Description
Name
Default Value
Step
Range
Function permission
Function
DISABLED
N/A
[DISABLED – ENABLED]
Snapshot event generation
Snapshot Events
ENABLED
N/A
[DISABLED – ENABLED]
Содержание F650
Страница 68: ...2 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 2 6 EXTERNAL CONNECTIONS CHAPTER 2 PRODUCT DESCRIPTION ...
Страница 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Страница 660: ...7 254 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 7 3 IEC 61850 CONFIGURATOR CHAPTER 7 IEC 61850 PROTOCOL ...
Страница 734: ...12 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 12 4 RELAY CONFIGURATION CHAPTER 12 FREQUENTLY ASKED QUESTIONS ...
Страница 772: ...A 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF A 1 OPERANDS F650 MODEL FX GX APPENDIX A LOGIC OPERANDS ...
Страница 950: ...c 24 F650 DIGITAL BAY CONTROLLER GEK 106310 AF C 8 ANALOG INPUTS APPENDIX C DNP 3 0 PROTOCOL FOR F650 ...
Страница 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Страница 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Страница 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Страница 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1044: ...I 40 F650 DIGITAL BAY CONTROLLER GEK 106310 AF I 2 FACTORY DEFAULT CONFIGURATION APPENDIX I FACTORY DEFAULT CONFIGURATION ...
Страница 1046: ...J 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF J 1 GE MULTILIN WARRANTY APPENDIX J MISCELLANEOUS ...