5-198
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
SYSTEM SETUP
CHAPTER 5: SETTINGS
5
Figure 5-100: Recloser curve initialization
5.5.6.4 Example
A composite curve can be created from the GE_111 standard with MRT = 200 ms and HCT initially disabled and then
enabled at eight times pickup with an operating time of 30 ms. At approximately four times pickup, the curve operating
time is equal to the MRT and from then onwards the operating time remains at 200 ms.
Figure 5-101: Composite recloser curve with HCT disabled
With the HCT feature enabled, the operating time reduces to 30 ms for pickup multiples exceeding eight times pickup.
The
Multiplier
and
Adder
settings only affect the curve portion of the characteristic and not the MRT and HCT
settings. The HCT settings override the MRT settings for multiples of pickup greater than the HCT ratio.
Содержание F35
Страница 12: ...1 4 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FOR FURTHER ASSISTANCE CHAPTER 1 INTRODUCTION 1 ...
Страница 202: ...4 88 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FLEXLOGIC DESIGN USING ENGINEER CHAPTER 4 INTERFACES 4 ...
Страница 562: ...6 30 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL PRODUCT INFORMATION CHAPTER 6 ACTUAL VALUES 6 ...
Страница 576: ...7 14 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL TARGETS CHAPTER 7 COMMANDS AND TARGETS 7 ...
Страница 650: ...A 38 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FLEXANALOG ITEMS APPENDIX A FLEXANALOG OPERANDS A ...
Страница 658: ...C 6 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL COMMAND LINE INTERFACE APPENDIX C COMMAND LINE INTERFACE C ...
Страница 666: ...iv F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL ABBREVIATIONS ...
Страница 682: ...xvi F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL INDEX ...